what should be the minimum rating for using HT Motors?
Answer / amit biswas
general kW Vs Voltage ternd for motors as as follows
upto 250 Kw -414V
250-450 Kw-3.3 KV
above 450 Kw-6.6 KV
anyways these standrds can be avoided but this will affect
the size of motor.eg.a 250kV motor rated at 6.6 Kv will be
smaller in size thanat 3.3KV
Is This Answer Correct ? | 4 Yes | 1 No |
IN A DY11 GROUP DISTRIBUTION TRANSFORMER WITH NEUTRAL EARTHED, WHAT WILL HAPPEN TO THE SYSTEM VOLTAGE & THE EQUIPMENTS IF EARTH GETS OPEN ON LOAD?
what will happen if we give a dc supply to a transformer.?
How much DC or AC Current that a Human Body withstand for Electrical Shocks?
could an induction motor be used for regenerative braking in electric-train control? in this type of application would some scheme have to be devised to obtain low synchronous speeds while braking? would induction-motor drive, therefore, be suitable for passenger service?
What is the difference between AVR and Servo Stabliser
why nearly all voltages are in the multiples of 11?
Why electrical heaters are not provided with overload relays in circuits
IF TVM OF TRANSFORMER SHOWS POWER FACTOR ON 33 KV SIDE AS 0.97 LAGGING AND ON 132 KV SIDE IS 0.75 LEADING.IS THIS CORRECT.WHERE IS PROBLEM.
According to underground cables a) stress b/w sheath & conductor is high b) inrush of core & conductor
0 Answers CDS, Engineers India Limited, TNQ,
lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???
a starter used for squirrel cage induction motor?
What will happen to the protection and metering, if the polarity of a single or two PT/PTs in three phase system is reversed? Please provide reference if any.