WHY DG are rated in KVA or MVA ???., but ALL power plants
are rated in KW or MW.,,?
Answers were Sorted based on User's Feedback
Answer / vithal k.
Power plant capacity is in MW means ultimately its in terms
of Amps, current and in PF.
Whereas DG is there in KVA means in terms of voltage and
current.
PP is directly connected to Grid and hence directly come in
to the picture with System inductance.. where as DG will
have bounded load and no more Inductive load is there
compared to Grid and hence negligibly considered as 1 (PF=1)
Ultimately in KW terms PF came out of picture and hence DG
rating ar3e normally in KVA.
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / rajsekhar mahapatro
All dg are rated in KVA but as other conventional power plants in kw because the dg's are local power plants they have to generate their own active and reactive power as well. But in modern power plants they are used to generate only the active component of power but not the reactive power, the reactive power required by the load is generated locally by using capacitors and other arrangement.So they are raked in KVA and KWs.
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / remodeen
MOSTLY POWER PLANTS ARE RATED SUCH THAT 210 MW., 600MW.,,
58MW.,,
BUT DG SET ALSO SAME THING BUT RATED IN KVA OR MVA.........
| Is This Answer Correct ? | 3 Yes | 16 No |
What is the difference between MPCB and OLR?
why DOL starter is use in induction motor as it is not reduce the starting torque
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
In case of motor Power Factor Generally We Apply A Capacitor But How Can We Know That A Motor is Running On Very low Power Factor And What Rating Of Capacitor We Have To Place And Tell Me Conversion Of Micro Farad to KVAR>
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
What is the difference between a verilog task and verilog function?
What is the calculating formula for HT and LT amps in a transformer.
what is current actully?significance of current...not rate of change of flow.....
How do the synchronizing lamps indicate the correctness of phase sequence between existing and incoming alternators?
what is meant by moulded case circuit breaker ?
What are the types of lighning arrestor protection system? how to choose that according to load?
how you will decide the distance between the power transformer and its fencing
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)