Answer / sss
To synchronise two or more generator it's frequency , phase sequence and terminal voltage should be same. ...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / e.subhash
If a.C generator means
The following condition should be same before synchronizing the generator (whatever it may be it's size)
1) bus voltage and machine voltage
2) bus frequency and machine frequency
3) bus and machine phase sequence
4) phase angle
The following method is using for synchronizing.
1) dark lamp method
2) bright lamp method
3) synchroscope method
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tasawar abbas suddle
When I sync. the two more than generator we must knowledge of the generator like as its frequency, phase seq, voltage magnitude & phase angel. and its capacity is also same.
if these generator capacity not same then when i start the generator will give the power to the system the other generator is small when big generator give the power to system and the other small generator will absorbed the power and it work like as motor.
and the second small generator will also absorbed power there is no benefit
| Is This Answer Correct ? | 0 Yes | 4 No |
I have a 25 KVar capacitor bank at my facility.How to check the capacitor bank ??
How does numerical relay work?
State thevenintheorem?
in Telecom DC system-why positive +ve is made earthed.and - ve is fed to load.
what will happen when ac is applied resistor,inductor,capcitor?
how to select the power contactor in Diffrent AC motors.
what is the difference between concentrated winding and Distributed winding in motor?
what is reasion of harmonic create the power supply , And how to reduced to harmonic
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?
In a large office how do we calculate required number of light fittings, assuming fittings are 4x18W or 2x36W fluorescent fitting ?
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
what is the ground fault relay,which purpose it will be use,clearly tell me plz
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)