How i can calculate the cable size for given load,there is any formula,for 3 phase and single phase
Answers were Sorted based on User's Feedback
Answer / jafar
for calculating cable size first we have to calculate load current
example 1 : 3KW POWER (1phase)
current i= 3*1000 /(230*0.8)
= 16.3A
for current carrying capacity of 1 sq mm copper is 2.4A
for current carrying capacity of 1 sq mm AL is 1.4A
now here if we use Cu then cable size is 16.3/2.4
= 6.79 is our calculated value
so we can choose near size of cable which is 10 sq mm
example 2 : 100W power (3 phase)
current i= 100*1000/(1.732*400*0.8)
= 180A
like that above
cable size is 180/2.4 = 75
so near size is 95 mm2
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / love kumar
for three phase copper cable is consider as 1sq mm ,3amp.
for aluminium cable 1sqmm -1amp
| Is This Answer Correct ? | 0 Yes | 0 No |
What is slip in induction motor?
why we use low kv lightining arrester in line for example 9 kv using in 11kv
Why did call copper as a electrical conductor?
What are the limiting factor for controlling maximum hot point temperature within a hydrogen and water cooled generator?
why transformer donot allow the dc?
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
how the diesel generator maintain the rpm when the generator loaded varies from 10% to 70% immediately?
Why we specify TNC switch with 1NO 1NC ,2NO 2NC ? how we get connection.?
What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you
1 Answers Power Grid, Vignan University,
short circuit test of transformer gives what?
how many types in CT & define it ?
Induction motor & transformer both has magnetic core,then why induction motor is a inductive load & transformer not???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)