What is the minimum permissive IR value for LT & HT motor for safe starting?
Answer / vinoth
IR means Insulation Resistance. basically IR value need is ( Rated KV+1 ) Mohm.
For eg if motor rated voltage is 11Kv then we need IR value has 12Mohm.
Minimum 1Mohm is sufficient to start LT motors.
For HT Motor- ( Rated KV +1)Mohm
it is very suffient to start motors
| Is This Answer Correct ? | 3 Yes | 0 No |
why and where we use early make & late break contacts in protection?
is there or does RCCB work for single phase connection?
If DC supply is given to a transformer it may a) Work b)Not Work c)Give lower voltage than the rated voltage on secondary side. d)burn the winding
why the generating / transmitting voltage is in the order of multiples of 11(ie 11kv,22kv,33kv......)
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
Igfet is a
why is use the star and delta connection and difference
what is bus pt and what is the function of it ???
I am getting diesel genset 62 kv for my house In addition there are 6 meters of 11kv for the house Lift also being installed for house plot sise 200sq yds total 4 + 2 foloors I want to know how much earthing required how deep it should be
How to Select transformer for 100HP motor plz... With calculation
Whay you want to change your job.
how a flip flop can be used as a latch?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)