how much load 15kva dg set can bear.with full explination
and how to calculate?
Answers were Sorted based on User's Feedback
Answer / amit chaudhary
The full load of 15 Kva DG set will be 12 KW on 0.8 power
factor. if the DG set is 3 phase(415 v) then per phase
current will be I = 15000/(1.732X 415)= 20.86Amp/PHASE
| Is This Answer Correct ? | 28 Yes | 8 No |
can you explain the rms value in simple words....
How many input terminal of single phase transformer.which is use for rural power distribution.
is there interlocking between duty and standby chilled water pumps?
It is advisable 2 use auto-transformer if transformation ratio is-a)110KV/11KV,b)230kv/110kv,c)110kv/66kv,d) 400kv/230kv
what will happen when square wave is fed into input side of 3kva transformer and what you will get on output side.
what meaning of gd squre
What is the range of the stator resistance of 3 phase induction motor?
Draw transformer phasor diagram.(full load,no load)
How to distinguish whether MCB is DC or AC looking at it physically
why earthing is not required on transformer prymary winding side ???
WHAT IS THE DIFFERENT BETWEEN MCB & MPCB? & HOW IS USE?
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)