how much load 15kva dg set can bear.with full explination
and how to calculate?
Answers were Sorted based on User's Feedback
Answer / amit chaudhary
The full load of 15 Kva DG set will be 12 KW on 0.8 power
factor. if the DG set is 3 phase(415 v) then per phase
current will be I = 15000/(1.732X 415)= 20.86Amp/PHASE
| Is This Answer Correct ? | 28 Yes | 8 No |
1.how many types of relays? 2.difference between ATS& STS?
how to calculate capacitor rating for an induction transformer ex.for 12 mva furnace calculate capacitor rating
What is a dc motor?
how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.
Is it necessary to install Lighting Arrester on both side side (i.e HT and LT) of Transformer in a transmission substation? if yes Why on both side?
Why we does earthing for transformer neutral point
what is meant by power and distribution transformer ?
How to Calculate IKW(input kilowatt)of a Chiller plant
what happenes if the core of the transformer saturates?
Relation between pyramids and electrical technology?
what is the difference b/w low voltage motors & medium voltage motors
When dc supply is fed to rotor of the alternator how it work?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)