Answer / santosh chinchalkar

If T.G set is running on synchronus speed and turbine is
triped on low steam pressure or some other resion, The
Generator will take the power from system instated of
giving and Generator will work as Motor,that will harmful
to Turbine blades.for avoiding this reverse power
protection are used to stop the Generator.

Is This Answer Correct ?    49 Yes 4 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / ashiesh

The gemneraTor wiLL start behaving as motor, & will consume
power instead of generating.
But will simply stop if it has a reverse power protection
system.

Is This Answer Correct ?    14 Yes 1 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / ramji

The Generator will run still since there some steam trapped
in Turbine.This suitation is called Low Forward Power since
there is not enough Steam to run the Generator in desired
speed.This occurs because of some trapped steam in turbine
for some seconds.Now Days special vents doors are designed
in turbine to release these steam on account of tripping of
turbines

But Normally in protection Trip Logic of Generators there
will be Class:A,Class:B,Class:C

For Class A Gen Breaker will trip for below faults
U/V Stage-2 , O/V , Low Forward Power,Reverse Reactive
power,Neg Ph Seq ,Over Voltage

For Class B Turbine Breaker will Trip which also trip Gen
breaker instantly for below faults

Differential protection , Restricted Earth Fault .....


For Class C Grid Breaker will trip for below faults

Over Frequency and Under Frequency Under Voltage stage-1
and Over voltage

Because when you trip Gen Breaker for Undervoltage it will
result in whole plant black out so for stage-1 tripping of
grid breaker will do

similarly for All turbine faults the Gen Breaker is tripped
so that it is isolated from the system

Is This Answer Correct ?    17 Yes 4 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / vivek

main breaker will be trip and annunciator will show
tripping prob.

Is This Answer Correct ?    10 Yes 0 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / dayal varma

automatically the output of the generator stop.

Is This Answer Correct ?    16 Yes 9 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / vikas kallewar

TURBINE RUNNING IN SOLO MODE. if turbine trip at that time
generator also trip. due to under frequency,under
voltage,and 86T WILL TRIP TO 86G.
TURBINE RUNNING IN PARRALAL MODE GENERATOR TRIP TO RPR
PROTECTION

Is This Answer Correct ?    5 Yes 2 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / arindam

When Turbine trips, the dc excitation voltage which is
applied to the rotor through slip ring also trips,so no
excitation was there in the rotor means no flux cutting in
the stator.So generating voltage will be zero. So it will
nither act as generator nor as a motor. Its simply rotate &
due to moment of inertia,it will come to zero in short time.

Is This Answer Correct ?    10 Yes 14 No

Post New Answer

More Electrical Engineering Interview Questions

In transmission line 11kv,33kv etc are rms values are peak or others??

1 Answers  


Star Delta Diagram with full description

0 Answers   SKS Microfinance, Syscom,


HOW DISTANCE PROTECTION IS DONE IN EHV TRANSMISSION LINES? WHAT IS THE BASIC TECHNIQ OR FUNDA USED BEHIND THIS ? SPECIALLY EXPLAIN?IMPEDANCE METHOD.

2 Answers   ABB,


what are the specifications for Dc cables of higher rating

1 Answers   Reliance,


i applied for c licence with my one year apperents trainee and i have attaced with A grade contractor company experiance that is for 14 monts experiance this document is sufeicant for c licence? pls tell why they rejected

0 Answers   TNEB Tamil Nadu Electricity Board,






Explain the Term in CT Name Plate – Class: 5Ps

3 Answers   Divis Laboratories,


16kv transformeris stolen in my village.and department is not taking action.then what should i do.any shortcut .please help any idea

1 Answers  


what is the working principle of soft-starter & how it diff. from VFD ?????????

5 Answers   L&T,


how many hvdc lines in india???

0 Answers  


Should the neutral earthing of 33/11KV D-S transformer, be connected to the earth grid?(Yes/ NO) why?

1 Answers   HAL, Vijai Electricals,


what is IMPEDENCE? FORMULE?

6 Answers  


i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)