WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?

Answers were Sorted based on User's Feedback



WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / santosh chinchalkar

If T.G set is running on synchronus speed and turbine is
triped on low steam pressure or some other resion, The
Generator will take the power from system instated of
giving and Generator will work as Motor,that will harmful
to Turbine blades.for avoiding this reverse power
protection are used to stop the Generator.

Is This Answer Correct ?    49 Yes 4 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / ashiesh

The gemneraTor wiLL start behaving as motor, & will consume
power instead of generating.
But will simply stop if it has a reverse power protection
system.

Is This Answer Correct ?    14 Yes 1 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / ramji

The Generator will run still since there some steam trapped
in Turbine.This suitation is called Low Forward Power since
there is not enough Steam to run the Generator in desired
speed.This occurs because of some trapped steam in turbine
for some seconds.Now Days special vents doors are designed
in turbine to release these steam on account of tripping of
turbines

But Normally in protection Trip Logic of Generators there
will be Class:A,Class:B,Class:C

For Class A Gen Breaker will trip for below faults
U/V Stage-2 , O/V , Low Forward Power,Reverse Reactive
power,Neg Ph Seq ,Over Voltage

For Class B Turbine Breaker will Trip which also trip Gen
breaker instantly for below faults

Differential protection , Restricted Earth Fault .....


For Class C Grid Breaker will trip for below faults

Over Frequency and Under Frequency Under Voltage stage-1
and Over voltage

Because when you trip Gen Breaker for Undervoltage it will
result in whole plant black out so for stage-1 tripping of
grid breaker will do

similarly for All turbine faults the Gen Breaker is tripped
so that it is isolated from the system

Is This Answer Correct ?    17 Yes 4 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / vivek

main breaker will be trip and annunciator will show
tripping prob.

Is This Answer Correct ?    10 Yes 0 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / dayal varma

automatically the output of the generator stop.

Is This Answer Correct ?    16 Yes 9 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / vikas kallewar

TURBINE RUNNING IN SOLO MODE. if turbine trip at that time
generator also trip. due to under frequency,under
voltage,and 86T WILL TRIP TO 86G.
TURBINE RUNNING IN PARRALAL MODE GENERATOR TRIP TO RPR
PROTECTION

Is This Answer Correct ?    5 Yes 2 No

WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?..

Answer / arindam

When Turbine trips, the dc excitation voltage which is
applied to the rotor through slip ring also trips,so no
excitation was there in the rotor means no flux cutting in
the stator.So generating voltage will be zero. So it will
nither act as generator nor as a motor. Its simply rotate &
due to moment of inertia,it will come to zero in short time.

Is This Answer Correct ?    10 Yes 14 No

Post New Answer

More Electrical Engineering Interview Questions

why the motor is rated as kw& transformer as kva

7 Answers   Areva,


what is the meaning of the symbol << >> put in transformer drawing

0 Answers   TATA,


How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.

0 Answers  


ELCP USE IN 3 PHASE SUBMERSIBLE PUMP? THEN USE 3 POLE 0R 4 POLE?

4 Answers  


What are all the points to be checked for a newly re-winded motor before installation

1 Answers   Cisco,






what is v/f control in VFD?

0 Answers  


please send me RRB electrical engineer previous year questions for Sr. Section Engineer

0 Answers  


How to calculate PF capactors for a connected load?

2 Answers   FD, Power World,


i asked a funny question in Electrical ohms law V=IR in const temp voltage is directly proportional to current Power p=VI cos@ in that formula Voltage is indirectly proportional to current Try to give me the fact what is happening in Electrical.. contact Thanigai_1984@yahoo.co.in

3 Answers  


hou we find and calculate the maximum lode capesity of transforer?

1 Answers  


ARE YOU NOURVAS ?

4 Answers  


how can we generate electricity????

6 Answers   Torrent Power,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)