why we use only 4-20 ma signal as AI and not 0-20 ma?
Answers were Sorted based on User's Feedback
Why we use 4-20mA signal?? Not start from 0-03mA? & 20mA??
· We can not use 0-20 mA signal cos then it becomes very difficult to distinguish between "zero" signal and "instrument fail" signal.
· Where as if we use 4-20 mA. its very easy like when we get 4mA means the signal is at low level and if it is below 4mA it shows us that the instrument is not working or it is failed
•That may have been one of those arbitrary decisions that is sometimes made when a standard is developed. In addition to providing a non-zero minimum to allow detecting signal loss, the minimum signal voltage provides for a margin between the minimum signal and any noise that might be present. Perhaps someone determined that 4ma was large enough to help with noise and thought that the numbers worked out conveniently. A 16 volt difference between min and max, difference = 4 X min, range of 20% to 100%, perhaps seemed easier to work with than 17 volts, 5.67 X min and 15% to 100% or 18V, 9 X & 10% to 100%
•This 20 mA signal is not enough to trigger a spark and therefore we can limit fire hazards in plant area
•As there is a leakage current so 0 to 3 MA, so we consider as 4-20MA. But in some cases we will find some transmitters 0-20MA which are more costly than 4-20mA
| Is This Answer Correct ? | 11 Yes | 0 No |
How to calibrate electronic type level switch low?
Instrumentation engineer please reply me,I am electrical engineer ,what is the future in instrumentation dept {presently working (P&ID) Design} for me,whether good future for me as instrumentation department.what side can i get job in future
What is meant by cold float of compressor shaft.
suppose there is gas flow meter I want to know weather meter calibration is done at high pressure or low pressure? pls justify.
Pressure tx shows 1 mbar but we need 1000 mbar at this process condition .. how can we sort it out .
where i can get training in INTOOLS and PDMS in Delhi-NCR OR north part of India. please reply with ur ans. at arunsamkaria@ymail.com
when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )
Hi Frnds , If Suppose 1 Pair cable of 1.5 sq mm is used for Transmitter and instead of 1.5 sq mm if i used 0.5 sq mm cable will the resistance change will occur and does it affect our transmitter reading. plz mail ur answer to ntnkamble@gmail.com plz immediately mail ur reply
WHAT IS THE MAIN WORKING OF BOILER.
what r all the type of viberation measurement measuring in turbin? what's the output of viberation sensor?
what is easiest way to read STL language in PLC?
Can anyone convert a 5/2 way or 3/2 way valve into an ISO valve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)