suggest a sensor to measure rapidly varying temperature?
Answer / p r j
What is your temperature range? if it is 0 to 500 deg. C
and no vibration in area then you can easly go for RTD with
transmitter and indicator.
How high temp. you can use J type thermocouple with
transmitter and indicator.
above 1000 dg c use K type for R type. While using
Thermocouple be carefull about Cold Junction Compensation.
Is This Answer Correct ? | 9 Yes | 0 No |
What s the exact height of installed transmitter?
difference between plc and dcs?
how can i communicate with non-national instruments device with pc via labVIEW8.2
3 Answers Google, Mico, National Instruments,
Q- Why Phase tester is only used for checking AC not DC ?
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
what is relation between electronics&instrumentation
WHAT REASEAN USE TRANSMETER TWO WIRE & FOUR WIRE
What is the difference between PLC-HMI and DCS as each function of DCS based system is possible in PLC ?
WHAT IS DIFFERANCE BETWEEN INSTRUMENT AND EQUIPMENT
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
How to convert milliampares into flow??