the total iron closs in a transformer core at normal flux density was measured at 25hz and 5ohz and was found to be 250w and 800w respectively.the hysteresis loss at 50hz would be................?????
Answer / utkarsh agarwal
according to the data flux density is constant.
Pe1=f1^2 Ph1=f1
Pe2=f2^2 Ph2=f2
takinf f1=25hz
f2=50 hz
Pe1/Pe2=1/4
Ph1/Ph2=1/2
now iron loss Pi=Ph1+Pe1
Therefoe
1. ph1 + pe1=250
2. 2ph1+ 4pe1=800
solving we get ph2= 200w
P.S. : "=" is meant to be proportiaonality sign in first 3 lines
| Is This Answer Correct ? | 8 Yes | 1 No |
why h parameter are called as hybrid parameter?
what are the highly demanded courses for electrical engg. who finished his b.tech
why using eleven's multiple for substations?
how fan speed decrease or increase by using regulator? thank you
What is the minimum distance to be maintained in between HT panel and LT panel and Instrument panel as per IEC and NEC standards?
What transistor level design tools are you proficient with? What types of designs were they used on?
What should be the minimum and maximum ohmic value for earthing?
Define de-sensitivity?
Name the instruments which run on DC?
What is DC power factor??
what is the formula to calculate the distance between one phase to another phase in single phase line and 3 phase line for different volt for example ; 33kv, 11kv ,22kv,230v
why do we carry out winding resistance test?
0 Answers MahaGenco, MAHINDRA,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)