the total iron closs in a transformer core at normal flux density was measured at 25hz and 5ohz and was found to be 250w and 800w respectively.the hysteresis loss at 50hz would be................?????
Answer / utkarsh agarwal
according to the data flux density is constant.
Pe1=f1^2 Ph1=f1
Pe2=f2^2 Ph2=f2
takinf f1=25hz
f2=50 hz
Pe1/Pe2=1/4
Ph1/Ph2=1/2
now iron loss Pi=Ph1+Pe1
Therefoe
1. ph1 + pe1=250
2. 2ph1+ 4pe1=800
solving we get ph2= 200w
P.S. : "=" is meant to be proportiaonality sign in first 3 lines
| Is This Answer Correct ? | 8 Yes | 1 No |
what are iron and copper losses
I did oil BDV test of 1600 KVA trafo 20KV/400V as per IEC 156. Result is 1) 58 KV 2) 58 KV 3)40 KV 4) 50 KV 5) 58 KV 6) 18 KV. Avr is 47 KV. Can we say oil is still ok even in the 6th test BDV is 18 KV ?
how can we connect the capacitor bank to improve the power factor?
For high frequency application we use which transformer?
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
why there is a phase difference between line voltage & phase voltage ?
PLZ sent the previous year question paper for GET in NHPC on my EMail id ppshanker@gmail.com
what is the working of hydrent system.
What do you meant by slip power recovery?
In hydro plant,generally we install vertical hydro generators..why dont we recommend horizontal one??
Why D.C Voltage used in Meggering...as well as in Hipot test? why not A.C?
what is power factor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)