the total iron closs in a transformer core at normal flux density was measured at 25hz and 5ohz and was found to be 250w and 800w respectively.the hysteresis loss at 50hz would be................?????
Answer / utkarsh agarwal
according to the data flux density is constant.
Pe1=f1^2 Ph1=f1
Pe2=f2^2 Ph2=f2
takinf f1=25hz
f2=50 hz
Pe1/Pe2=1/4
Ph1/Ph2=1/2
now iron loss Pi=Ph1+Pe1
Therefoe
1. ph1 + pe1=250
2. 2ph1+ 4pe1=800
solving we get ph2= 200w
P.S. : "=" is meant to be proportiaonality sign in first 3 lines
Is This Answer Correct ? | 8 Yes | 1 No |
how to calculate vfd o/p voltage by frequency
what will happen if a part of primary winding of a transformer is accidentally short-circuited?
cb used in railway applications is?
can d.c.transformer exist? if yes then what its max. rating?
what is meant by moulded case circuit breaker ?
HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER FEEDER AT START AND RUNNING?
In power plants the reading changes abruptly to give value (MW -25) (MVAR -15) What are the reasons for this? What is the solution?
how to calculate the current capacity of a wire if its dimension in Square mm is given
what is specific gravity of a battery if specific gravity increase/decrease,what will happen to the voltage/current of the battery
How to calculate the actual 3phase power, if the load current of each phase is not balanced
what is the difference between isolation and insolation ? please explain in detail with example.
what is the formula for building wiring to get the main breaker.