why the secondary current transformer cannot left open
Answer / subbu
Since ct is step up transformer ,with secondary open , very high voltage will develop on secondary side. Due to this high voltage , secondary winding insulation will fail .this will lead to damage of secondary winding.
Is This Answer Correct ? | 8 Yes | 1 No |