how to adjust relay in smart positioner ?
Answer / ralu
Steam Service (Filling the water legs)
1. Ensure that the steam line is depressurized with no steam.
2. Check the transmitter for a dry zero of 4 mA with no water loss.
3. Attach hose connection valve to high side vent DVH. See Figure 3-3.
4. Attach a water supply to the hose connection. The water supply
should have a maximum psi of 100.
5. Open the high and low manifold valves MH and ML and equalizer
valve ME (MEH and MEL for 5-Valve Manifolds).
6. Ensure low side vent DVL is closed.
7. Open the hose connect valve for a minimum of 30 seconds.
Water will flow through both the high and low chambers and
into the pipe.
8. Close the high side manifold valve MH for 30 seconds to force water
to the ML side.
9. Re-open the MH valve.
10. Open low side vent DVL until no air is observed.
11. Close the low-side vent DVL.
12. Close the hose connect valve and remove hose.
13. Close both manifold high side valve MH and manifold low side valve
ML.
14. Check the transmitter zero by noting the output. If the signal reads
outside of the range 3.98 mA to 4.02 mA, air is probably still in the
system; repeat this procedure from step 2, and trim sensor if
necessary.
15. Open the manifold high side valve MH.
16. Close equalizer valve ME (for 5-Valve Manifolds first close valve
MEL, then close valve MEH).
17. Open the manifold low side valve ML. The system is now operational.
| Is This Answer Correct ? | 0 Yes | 3 No |
What is input and output of vaiberation transmitter and what is its unit.
How much should be the values and/or percentages of these given below factors for a good controller ? Steady state error Delay Rise Time Overshoot Peak Time Settling Time Damping Oscillations & vibrations thanks
Can anybody please let me know Orifice plate sizing calculation formula and step by step procedure
what is loop1 and loop2 in MTS LT?
what is the difference between sinking and sourcing inputs and also what are there applications?
how to measure low temperature(<100 dec celsisus) with non condact sensor
hello sir/madam, I,Subramanian need 5yrs placement papers of officer trainee of Instrumentation technology.pls send to this mail id mani_nxtgen@yahoo.co.in please do the needful. with regards, subramanian.v
How to Calibrate variable Head flowmeter (Orifice), here we dont know High pressure and low pressure then how to apply pressure on HP and LP side ?
The document / drawing that is primarily used in depicting the “Bill of Materials (BOM)” of piping system is the
Basically iam Instruemntation Engineer, but Iam interested in Instruments design engineering, so plz guide, is there any course, training or Softwres to become Instrument design engineer??.
0 Answers Honeywell, Tata Steel Limited,
What is zero elevation and zero suppression?
How to calibrate radar type level transmitter for interface level? Total liquid(liq.1 and liq.2), level both the liq individually? For. Both the liquid levels how the signal will go from transmitter to dcs? How to calibrate. Single radar 9:26:55 AM for 2 different liquids in a tank?
0 Answers Almeer Technical Services,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)