how to adjust relay in smart positioner ?
Answer / ralu
Steam Service (Filling the water legs)
1. Ensure that the steam line is depressurized with no steam.
2. Check the transmitter for a dry zero of 4 mA with no water loss.
3. Attach hose connection valve to high side vent DVH. See Figure 3-3.
4. Attach a water supply to the hose connection. The water supply
should have a maximum psi of 100.
5. Open the high and low manifold valves MH and ML and equalizer
valve ME (MEH and MEL for 5-Valve Manifolds).
6. Ensure low side vent DVL is closed.
7. Open the hose connect valve for a minimum of 30 seconds.
Water will flow through both the high and low chambers and
into the pipe.
8. Close the high side manifold valve MH for 30 seconds to force water
to the ML side.
9. Re-open the MH valve.
10. Open low side vent DVL until no air is observed.
11. Close the low-side vent DVL.
12. Close the hose connect valve and remove hose.
13. Close both manifold high side valve MH and manifold low side valve
ML.
14. Check the transmitter zero by noting the output. If the signal reads
outside of the range 3.98 mA to 4.02 mA, air is probably still in the
system; repeat this procedure from step 2, and trim sensor if
necessary.
15. Open the manifold high side valve MH.
16. Close equalizer valve ME (for 5-Valve Manifolds first close valve
MEL, then close valve MEH).
17. Open the manifold low side valve ML. The system is now operational.
Is This Answer Correct ? | 0 Yes | 3 No |
what is effect of specific gravity in differential level transmitter , explain formula related with this .
0 Answers Flour Tech Engineers (P) Ltd,
What is the difference between sdv and bdv ?
What is the difference in clamp on type and inline type ultrasonic flow transmitter.
i want the equation of this question. Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
how checking is done in fiber optic cable? explain the working of RTU?
what is three element loop
what r all the closed loop used in boiler? for this related tell some web address..
Briefly describe instrumentation job
what is the difference between laminor flow and turbulant flow
How to convert 0-2500mmH2o into kg/hr? Or how to convert mmH2O into kg/hr,t/hr etc
what is the deluge ? How can its working?
What are the maximum packet size of: a) HART b) Profibus DP c)Profibus PA d) DeviceNet e) Foundation Fieldbus