Answer / shan80
it depend upon the value of current flows during short
circuit.
And the short circuit current depends upon the KVA rating of
transformer how supplies that particular load and transformer
percentage impedance.
| Is This Answer Correct ? | 56 Yes | 15 No |
Answer / jitesh patel
we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.
Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.
| Is This Answer Correct ? | 79 Yes | 50 No |
Answer / mohammed rafi
All above said suggestions are mere copy paste of something from wiki answer.its totally wrong.
Aforesaid calculations are to calculate rated current.
Short circuit analysis is to be done to calculate breaking capacity.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / ranadhir roy
We need to find out the short circuit MVA & based on this shortcircuit MVA , we need to calculate shortcircuit current .
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sunil sethi
All are ok, but In industries generally 5MVA transformer they are using for a company load, then if we consider 5MVA is our load then Icu is 5/(1.732x440)=0.0065ka , please clarify, Is it ok please answer .
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / t s gupta
Breaking Capacity of MCCB is pre-calculated permissible amount of fault current (value of current can flow from contacts before opening/tripping the MCCB without damaging) which may facilitate the safe operation of MCCB and distribution transformer both.
It shall be calculated/derived from the distribution Transformer MVA rating and %impedance = kVA*100/ system voltage of load side * % Impedance rating
e.g. 20 kVA transformer with 5% Impedance, secondary voltage 440V i.e. 0.440 kV
Fault current Isc = 20*100/.440*5 = 10kA approx.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / hrusikesh dehury
we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.
Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.
| Is This Answer Correct ? | 14 Yes | 24 No |
WHY IS THE POWER FACTOR NOT MORE THAN UNITY.
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
WHY DIODE IS CONNECTING ACROSS SWITCHES
how to calculate cable size with respect kw
TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?
What are various accuracy classes of CT(Current Transformer)
How we do the maintenance of Servo motor, even we cant open it?
what is load balancing. what maximum load diffence is allowed between phases.
clarify types of motor operated valves and advantages
Why auxiliary transformers are not connected in parallel in primary stations?
how mass curve differs from hydrograph.
Hi friends. is it possible that SCADA System through RTUs can connect Via PLCC Communication carriers ? thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)