How to calculate the breaking capacity(like 15ka,20ka) of
Circuit breaker (MCB,MCCB,ACB)
Answers were Sorted based on User's Feedback
Answer / shan80
it depend upon the value of current flows during short
circuit.
And the short circuit current depends upon the KVA rating of
transformer how supplies that particular load and transformer
percentage impedance.
| Is This Answer Correct ? | 56 Yes | 15 No |
Answer / jitesh patel
we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.
Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.
| Is This Answer Correct ? | 79 Yes | 50 No |
Answer / mohammed rafi
All above said suggestions are mere copy paste of something from wiki answer.its totally wrong.
Aforesaid calculations are to calculate rated current.
Short circuit analysis is to be done to calculate breaking capacity.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / ranadhir roy
We need to find out the short circuit MVA & based on this shortcircuit MVA , we need to calculate shortcircuit current .
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sunil sethi
All are ok, but In industries generally 5MVA transformer they are using for a company load, then if we consider 5MVA is our load then Icu is 5/(1.732x440)=0.0065ka , please clarify, Is it ok please answer .
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / t s gupta
Breaking Capacity of MCCB is pre-calculated permissible amount of fault current (value of current can flow from contacts before opening/tripping the MCCB without damaging) which may facilitate the safe operation of MCCB and distribution transformer both.
It shall be calculated/derived from the distribution Transformer MVA rating and %impedance = kVA*100/ system voltage of load side * % Impedance rating
e.g. 20 kVA transformer with 5% Impedance, secondary voltage 440V i.e. 0.440 kV
Fault current Isc = 20*100/.440*5 = 10kA approx.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / hrusikesh dehury
we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.
Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.
| Is This Answer Correct ? | 14 Yes | 24 No |
hi frienda We have 750kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
What is the diffrence (Technical & Construction ) between CBCT & Normal CT?
Why is it that polarization index type test is required for MV and HV motors and not for LV motors?
3 Answers La-Gajjar Machineries, Qatar Airlines,
what is tesla ?
what is full form of google
what is the significance of terminal voltage and phase sequence in the operation of paralleling of two generators?
what is fault level of power system ?
Which motor will you choose which can operate in both lagging as well as leading power factors?
how we check vector group dyn7
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase, before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
In my home i am getting too much electricity bill (more than 4000) but I am very much sure that we are not consuming that much. How i can check this ?
What are HT & LT Cables? What are their values?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)