Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the breaking capacity(like 15ka,20ka) of
Circuit breaker (MCB,MCCB,ACB)

Answers were Sorted based on User's Feedback



How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / shan80

it depend upon the value of current flows during short
circuit.
And the short circuit current depends upon the KVA rating of
transformer how supplies that particular load and transformer
percentage impedance.

Is This Answer Correct ?    56 Yes 15 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / jitesh patel

we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.

Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.

Is This Answer Correct ?    79 Yes 50 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ali

100A MCCB Bteaking capacity calculation

Is This Answer Correct ?    16 Yes 4 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / mohammed rafi

All above said suggestions are mere copy paste of something from wiki answer.its totally wrong.
Aforesaid calculations are to calculate rated current.
Short circuit analysis is to be done to calculate breaking capacity.

Is This Answer Correct ?    11 Yes 3 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ashok

it depends on the short circuit & full load of equipment

Is This Answer Correct ?    24 Yes 20 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ranadhir roy

We need to find out the short circuit MVA & based on this shortcircuit MVA , we need to calculate shortcircuit current .

Is This Answer Correct ?    2 Yes 0 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / sunil sethi

All are ok, but In industries generally 5MVA transformer they are using for a company load, then if we consider 5MVA is our load then Icu is 5/(1.732x440)=0.0065ka , please clarify, Is it ok please answer .

Is This Answer Correct ?    2 Yes 3 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / t s gupta

Breaking Capacity of MCCB is pre-calculated permissible amount of fault current (value of current can flow from contacts before opening/tripping the MCCB without damaging) which may facilitate the safe operation of MCCB and distribution transformer both.
It shall be calculated/derived from the distribution Transformer MVA rating and %impedance = kVA*100/ system voltage of load side * % Impedance rating
e.g. 20 kVA transformer with 5% Impedance, secondary voltage 440V i.e. 0.440 kV
Fault current Isc = 20*100/.440*5 = 10kA approx.

Is This Answer Correct ?    0 Yes 1 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / hrusikesh dehury

we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.

Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.

Is This Answer Correct ?    14 Yes 24 No

Post New Answer

More Electrical Engineering Interview Questions

Why is back emf used for a DC motor? Highlight its significance.

0 Answers   ABB,


whats is the role of power factor in designing a tariff structure?

1 Answers   IIT,


To avoid arcing what we connect in earthing.

4 Answers   HAL,


Can I Drain A Oil For Sample When The Transformer is Running? (Charged)

2 Answers  


what is the difference between single phase, 2 phase, and 3 phase in electric meter?

1 Answers  


what sort of general awareness questions are asked in o.n.g.c entrance exam?????????????????

0 Answers  


Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT? 

0 Answers  


what is different between synchronous & asynchronous motors

3 Answers  


I am an electrical engineer, I found variation in KWH between DG and EB for Same load for same duration, can any one help me why this variation arises?

1 Answers  


Why substation battery room is coulered black?

1 Answers  


what are the deffects for failure of PLC?

0 Answers  


What is voltage in two phase?

7 Answers   ABB, SSG,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)