Answer / shan80
it depend upon the value of current flows during short
circuit.
And the short circuit current depends upon the KVA rating of
transformer how supplies that particular load and transformer
percentage impedance.
Is This Answer Correct ? | 56 Yes | 15 No |
Answer / jitesh patel
we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.
Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.
Is This Answer Correct ? | 79 Yes | 50 No |
Answer / mohammed rafi
All above said suggestions are mere copy paste of something from wiki answer.its totally wrong.
Aforesaid calculations are to calculate rated current.
Short circuit analysis is to be done to calculate breaking capacity.
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / ranadhir roy
We need to find out the short circuit MVA & based on this shortcircuit MVA , we need to calculate shortcircuit current .
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sunil sethi
All are ok, but In industries generally 5MVA transformer they are using for a company load, then if we consider 5MVA is our load then Icu is 5/(1.732x440)=0.0065ka , please clarify, Is it ok please answer .
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / t s gupta
Breaking Capacity of MCCB is pre-calculated permissible amount of fault current (value of current can flow from contacts before opening/tripping the MCCB without damaging) which may facilitate the safe operation of MCCB and distribution transformer both.
It shall be calculated/derived from the distribution Transformer MVA rating and %impedance = kVA*100/ system voltage of load side * % Impedance rating
e.g. 20 kVA transformer with 5% Impedance, secondary voltage 440V i.e. 0.440 kV
Fault current Isc = 20*100/.440*5 = 10kA approx.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / hrusikesh dehury
we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.
Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.
I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.
Is This Answer Correct ? | 14 Yes | 24 No |
My load is 15 kw,i want to improve power factor from 0.8 to 0.9,how select capacitor
What is the difference between single point and double point bonding. please kindly detail about bonding of cables.
difference b/w series¶llel
As i want some model question paper in basic computer science and history please send me immediately sir
0 Answers TNPSC Tamil Nadu Public Service Commission,
We have two APFC panels in same station. I need how to connect CT in two APFC panels.can we take one CT in series connection or two separate CTs.
is it possible to have dc motors on single chip
HOW TO FIND THE PRIMARY AND SECONDARY OF TRANSFORMER(IN OFF CONDITION) USING MULTIMETER? IS IT POSSIBLE FIND BY SEEING RESISTANCE???
Does the dg syncronization sucessful in practical.
WHAT IS THE DIFFERENCE BETWEEN NEUTRAL AND EARTHING
1 Answers Adani, Adani Power, Raychem RPG,
What is tan delta point of transformer?
What is the formula for calculating the Instantaneous Short Circuit & overcurrent for any breaker
what do you mean by class PS CT and what are technical details needed for calculating it?