Pls.could any one Clarify the following with an example.

1.At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.
2.If Pressure is abnormal as per set pressure,if connecting
Terminal of pressure switch breaks,how the voltage extends
to Relay base.
3.Are these contacts come under fail safe philasaphy.



Pls.could any one Clarify the following with an example. 1.At What condition Close on Rise and Cl..

Answer / carl_ellis

1. At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.

Close on Rise: the goal is to detect overpressure in normal
operation.
Common to NO is 'made' in the alarm state, logic high state.
Common to NC is open in the alarm state, a logic low state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state.

Close on Fall: the goal is to detect and signal loss of
pressure in normal operation
Common to NO is 'made' in the alarm state.
Common to NC is open in the alarm state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state

2. If Pressure is abnormal as per set pressure, if
connecting Terminal of pressure switch breaks, how the
voltage extends to Relay base.

A pressure switch is wired directly to the wiring terminals
on the microswitch inside the pressure switch. There is no
'relay base' that I'm aware of.

For normal operation (the Common and the NO contact), either
broken wire will leave the electrical circuit in a logic low
state (no voltage).

In normal operation an alarm state is a logic high condition
(the presence of voltage). That means that a broken wire
open circuit can not conduct a voltage, which means that the
circuit will have a logic low state and will fail to detect
an alarm condition.

If the circuit is wired fail-safe (the Common and the NC
contact) a broken wire creates an open circuit that cannot
conduct voltage so the circuit will be in a logic low state
(the absence of voltage) which is the same as an alarm
condition, a logic low state.

3. Are these contacts come under fail safe philasaphy.

Fail Safe is accomplished by

a) wiring to the Normally Open (NO) contacts (Common to NO
is 'made' when there is an absence of pressure) and

b) having the logic solver look for an alarm condition or a
fail condition in the logic low state.

Either the absence of pressure or an alarm state will
produce a logic low, whether the setpoint is set for
close-on-rise or close-on-fall.

Fail-safe pressure switch wiring can not detect failure
conditions like a plugged impulse line or a valve-blocked
impulse line, with the exception of United Electric's ONE
series electronic pressure switch which has plugged port
detection and an I-AM-WORKING signal mode.

Carl Ellis
Measure First

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

How much voltage we get between two wire of 4 to 20 ma output? Is this voltage up or down respectvice to 4 - 20 ma ?

9 Answers  


How flow can be measured with dp?

0 Answers  


kindly tell where orifice,nozzle,air foil,ventury used in flow measurement?

1 Answers  


what is the difference between venturi and orifice meters?

9 Answers   Medha Servo Drives,


how to wire from pressure transmitter to marshalling panel and panel to controller and controller to dcs plz give the answer with example .

2 Answers  






Why boiler chimney area  oxyden sensor fixing? 

0 Answers   NTPC,


purpose of absolute ppressure transmitter applcation?

1 Answers  


I have completed B.E. Instrumentation & control in 2009. i have 3 year industrial job experience in chemical plant.now, I want to join M.E. in external. so, Plese say easiet way and good institute name.

0 Answers  


What is sensitivity of K type thermocouple? Is polarity important in thermocouple connections?

3 Answers   Honeywell,


I need circuit for RTD senser?

0 Answers  


given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)

0 Answers  


What for barriers are used in DCS & PLC systems?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)