in star delta starter current is 1/3times the delta value
how?
Answers were Sorted based on User's Feedback
Answer / parag bijlani
In star-delta starter, motor starts in star, and after a
time delay ,it switches to delta connections. The star
current is 1/1.732 (square root of 3).
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / amit kumar singh
in delta conection motor is direct on line current is
controled by relay in curcuit starting current high so used
high tourq motor as conveyr belt drive,water pump.use for
low hp motor.
in star delta conection current is redused 1/square root of
three, havey hp motor for protection heating low current is
requrid so we use star delta starter. its used for high hp
motor.
component in delta- one contactor,fuse,pushbutoon off-
on,field coil,overload relay.
component in star-3 contactor,fuse,pushbutoon, under
voltage coil,overload relay
Is This Answer Correct ? | 4 Yes | 3 No |
why do we have 230v a.c. as general voltage for domestic supply rather than others?
What do you mean by Transformer?
9 Answers Hyundai, NTPC, wbsedcl,
In a generator (Synchronous) does the rotor speed (frequency) corresponds to the speed of the water (in hydro). does the torque on the turbine relate to the flow of water?
what is mean by xlpe swa pvc
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
What is emperical relation.Name few of them which are used in electriacl engineering?
what is the voltage regulation constant of ACSR Raccoon conductor
If the kvar rating of capacitor bank is 600 kvar at 525V then what it's rating at 415v.
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
which one has maximum efficiency autotransformer or transformer?? and why??
List examples of current sources?
what are the stresses in circuit breakers ?