Guy's need your support,I want to measure closed tank level which is under vacuum -630mmHg using DP Transmitter, tank fluid density 1.38, Tank height is 7ft
Answers were Sorted based on User's Feedback
In such case vaccume will apply in both lags equally .
Now hight is 7 ft and density 1.38
7 ft is equal to 84 inches
So ,
84 X 1.38 = 115.92 inches of H2O became our span.
1 inches of H2O = 1.87 mmHg
Thus,
115.92 inches H2O = 216mmHg
tank is closed thats why ,
LRV = - 216 mmHg
URV = 0 mmHg
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sr
mothods of measurements don't change with change in line pressures ... the methods r same for both +ve and -ve pressure .... in vacuum u just have to take care that vacuum shud not break ....
| Is This Answer Correct ? | 1 Yes | 0 No |
A differential pressure transmitter is required to correct for vacuum pressure. The DP's low side is installed high up, tapped into the vacuum and the DP's high side tapped in near the bottom.
The DP transmitter's minimum range (LRV) is zero
The DP transmitter's maximum range (URV) is:
maximum level height (inches or mm) * specific gravity
Liquid level = measured pressure in water column units (inches or mm) / specific gravity
Many digital indicators just scale the 4-20mA to the desired level range; so a calculation involving specific gravity isn't needed.
For example:
4.0 mA = 0.0 inches level
20.0 mA = 84.0 inches level
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 4 No |
Any one can help me to identified, how can we interchange the device in FF
PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..
can you suggest good traning institute in instrumentation ? (in automation, or designing)
How would i calibrate a new commissioned flow transmitter???
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
what is the difference between dcs & plc
what is the advantage by using PID controller than P& PID?
how do calibrate the valves.. with clear manual
what is the diffrence between mmwc and kg/cm2 for pressure measurment when we are using mmwc and when kg/cm2 and why????? ?? what is the reason
19 Answers Ecoboard, Jindal, Sepco,
What is use of condensate pot
5 Answers Alstom, Petrocil, Samsung,
what is maximum temprature in instrumentation
what is a good line as ic engineer as maintenance ,oc, project, calibration ,validation engineer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)