How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
Answer / abdul rahman
Each unit as in each flat 5kw ?? That would be 250kw for 50 flats.
250kw into 1.8 would be total current = 450amps
Cable sizing Acc to Dubai STDs for 450amps would be
2runs x 4C 150sq.mm Cu + 1C 150sq.mm ECC
Transformer sizing u need to take into account 20-25% future use efficiency of t/f and diversity factor
So for 250kw it would be 250x1.2x.8/.9 nearly 300kva transformer.
| Is This Answer Correct ? | 4 Yes | 0 No |
how to differentiate a mpcb,mcb with a contactor? Explain their working operation
What are approaches to tackle sedimentation problem of reservoir?
describe the Tranformer testing procedure
what is S.T?specify the range?
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
refrigeration cycle?
1 Answers MAHINDRA, Shapoorji Pallonji Group(SPCL),
can we start slipring motor on star delta like we start induction motor ? if yes where will we connect ?
We order Dyn 5 distribution transformer to a company. What arrives is Dyn 11. Is it ok to use this transformer. It will be installed alone.
why pure sine wave inverter used for desktop ?
why transformer rating is in kva?
What is the diffrence between PL Lamps and CFL Lamps
what is the function and use of oil filled cables specify its advantages and disadvantages
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)