How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
Answer / abdul rahman
Each unit as in each flat 5kw ?? That would be 250kw for 50 flats.
250kw into 1.8 would be total current = 450amps
Cable sizing Acc to Dubai STDs for 450amps would be
2runs x 4C 150sq.mm Cu + 1C 150sq.mm ECC
Transformer sizing u need to take into account 20-25% future use efficiency of t/f and diversity factor
So for 250kw it would be 250x1.2x.8/.9 nearly 300kva transformer.
| Is This Answer Correct ? | 4 Yes | 0 No |
Describe the colour rendering properties of i) tungsten filament lamps ii) tubular fluorescent lamp
why m and c are shorted in wattmeter
State the points to be considered for selecting a particular type wiring.
WHY MOSTLY BATTERY VOLTAGE IS IN MULIPLE OF 2 LIKE 2V,4V,8V,16V,18V....
How current is reduced in STAR connection?
what happens if DC earthing and AC earthings are shorted?
How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer
TO CALCULATE THE RESISTANCE OF GRR OF HT MOTOR 400KW WHEREAS STATOR VOLTAGE 6.6KV AND ROTOR VOLTAGE 705V AND ROTOR CURRENT IS 346A.
what is non uniform load
how to calculate voltage regulation?
how to identify vector group of three phase transformer by voltage method?
Is there any question in the name of Static Switch in UPS??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)