Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer



How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,tr..

Answer / abdul rahman

Each unit as in each flat 5kw ?? That would be 250kw for 50 flats.
250kw into 1.8 would be total current = 450amps
Cable sizing Acc to Dubai STDs for 450amps would be 
2runs x 4C 150sq.mm Cu + 1C 150sq.mm ECC 

Transformer sizing u need to take into account 20-25% future use efficiency of t/f and diversity factor

So for 250kw it would be 250x1.2x.8/.9 nearly 300kva transformer.

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

differentional compound gernater used for wielding porpose. why????????//

2 Answers  


What are the components ofan HT panel in a 11kv power station?

2 Answers   Reliance,


how the magnetic flux is said to be rotating & alternating?

4 Answers  


I have AC automatic voltage regulator 15KVA What output currant?

3 Answers   Siemens,


WHAT IS MEAN BY MAGNETIC LOCKING

3 Answers   Bhel,


how to compare with Relay settings for HT&LT panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps

0 Answers  


why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?

0 Answers  


how we can to the synchronization in transformer. What are the conditions for that.

1 Answers  


What is the difference b/w Earthing and Grounding?

4 Answers  


our scope called one core cable for distribution system so we like to use 4 core cable with one equipment grounding conductor so what kind of technical reasons i can say that the 4core is better then 1 core,

2 Answers   Elite Construction,


wil a dc motor run without a starter??

9 Answers   MRF,


What is rotor angle stability?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)