When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok.
So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?

Answers were Sorted based on User's Feedback



When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct fr..

Answer / k.prakashchandra

100 W bulb draws about 0.5 A , hence the voltage drop for 5 ohm ER is about 2.5 V which is not noticeable . For 10 A load , the drop would be about 50 V .

Is This Answer Correct ?    2 Yes 2 No

When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct fr..

Answer / karthick

Because, neutral volt is '0'v when the phase is increase neutral volt also increase so neutralvolt reduce though earth

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Why is a plain induction motor unsuitable for wide speed control?

0 Answers  


which stabilizer is better ? AVR, Servo Stabilizer, Static stabilizer etc & why explain it

0 Answers  


We have isolation transformer 25kvA & ONLINE UPS 15KvA (3PHASE I/P,3PHASE O/P)where isolation should have connect,before UPS or after please brief.

1 Answers   DRJ ARDE,


what is the definition of a power transformer ?

4 Answers  


what happen ehen synchronisation is done at below rated speed

0 Answers  






what is distribution board and panel board

3 Answers  


What is the accepted limit to increase the choosen transformer capacity over the load and why ?

2 Answers   Asec,


Please mention any books for electrical design load calculation for industrial,commercial(to select cable,breaker,bus bar,stator,)

1 Answers   C&S,


How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.

0 Answers  


why earthing is not required on transformer prymary winding side ???

13 Answers   Genpact,


can the measured percentage error during calibration of single phase energy meter be negative?

0 Answers  


Ohms law explain

1 Answers   Hetero,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)