When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok.
So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
100 W bulb draws about 0.5 A , hence the voltage drop for 5 ohm ER is about 2.5 V which is not noticeable . For 10 A load , the drop would be about 50 V .
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / karthick
Because, neutral volt is '0'v when the phase is increase neutral volt also increase so neutralvolt reduce though earth
Is This Answer Correct ? | 0 Yes | 3 No |
Why is a plain induction motor unsuitable for wide speed control?
which stabilizer is better ? AVR, Servo Stabilizer, Static stabilizer etc & why explain it
We have isolation transformer 25kvA & ONLINE UPS 15KvA (3PHASE I/P,3PHASE O/P)where isolation should have connect,before UPS or after please brief.
what is the definition of a power transformer ?
what happen ehen synchronisation is done at below rated speed
what is distribution board and panel board
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
Please mention any books for electrical design load calculation for industrial,commercial(to select cable,breaker,bus bar,stator,)
How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.
why earthing is not required on transformer prymary winding side ???
can the measured percentage error during calibration of single phase energy meter be negative?
Ohms law explain