Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this harmful for moter winding
Answer / ll.krishna rao
V=4.44fNBA Therefore V is proportional to frequency if you want not to exceed the design parameter of flux density.If you operate a motor at 50Hz instead of its rated 60 Hz,then you will be exceeding the flux density by 120% for 380 v
operation.I suggest you to operate the motor at 380/1.2 volts instead at the expense of full power.
Is This Answer Correct ? | 2 Yes | 0 No |
which protection are used for turbo generator in thermal power plant.
in electrical control panel. how can i choose the cable rating. (example - 11kw motor, 18-25A mpcb}
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
Which material is used for the core of a transformer and why?
In three phase energymeter the spindle rotating backward why?
Why the output of generator varies eventhough the shaft speed is constant in thermal power plant?
what are types of ups?
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
How does a star connection and delta connection work? How does the star connection save starting current and how does it change to delta?
As a good company employee, can you report your supervisor to the company management if he or she is going against the company interest in his or her actions?
how to calculate the Neutral transformer impedance?
why asa method ZPF method is more accurate than ASA method?