I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
Answer / carl_ellis
A closed pressure vessel requires a differential pressure
measurement in order to compensate for the pressure or
vacuum in the vapor space above the liquid.
The density is said to be 1, so we'll assume that what was
really meant is that the specific gravity is 1.00, the same
as the specific gravity of water. The measurement can be
made in engineering units of mm of water column (wc) with no
compensation for a specific gravity other than water.
A DP transmitter measurement:
(high side pressure) minus (low side pressure)
The low side pressure reading is (vacuum pressure).
The high side pressure reading is (column of water pressure
+ vacuum pressure)
(water column pressure + vacuum pressure) minus vacuum
pressure = water column pressure.
With a vertical elevation difference between the flanges of
440mm, the water column pressure will be
0 - 440mm wc.
LRV = 0.0 mm wc
URV = 440 mm wc
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
what is stroke check for field instument transmetter's & AOV's
What are the instrumental diagram of valve.
whether radar level transmitter is applicable for the open tank
any thing about plcs?
How to find out turn down ratio of Pressure transmitter?
In control valve there are two type of valve seat we can use metal to metal seat & soft seat.On this valve seat i have following doubt. 1)I have never seen practically the internal assembly of valve so my doubt is that basically weather the seat is soft seat or metal its basic MOC is same as valve body(SS or CS) only in soft seat we are using PTFE ring & place on valve seat & in metal this PTFE ring is not threr am i correct??????? 2)what are the common general rule for using metal to metal seat & soft seat,means its depend on process parameter like liquid,gas, steam & on valve leakage class.
what is diffrance between FF & SMART, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
how to calculate signal cable sizing? and multipair cable sizing??explain in brief?
PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS
Please can anybody tell me the step by step procedure for calibrating the Pr,Lvl,Fl,Temp transmitter on process?
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.
how to make temperature closed loop
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)