I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
Answer / carl_ellis
A closed pressure vessel requires a differential pressure
measurement in order to compensate for the pressure or
vacuum in the vapor space above the liquid.
The density is said to be 1, so we'll assume that what was
really meant is that the specific gravity is 1.00, the same
as the specific gravity of water. The measurement can be
made in engineering units of mm of water column (wc) with no
compensation for a specific gravity other than water.
A DP transmitter measurement:
(high side pressure) minus (low side pressure)
The low side pressure reading is (vacuum pressure).
The high side pressure reading is (column of water pressure
+ vacuum pressure)
(water column pressure + vacuum pressure) minus vacuum
pressure = water column pressure.
With a vertical elevation difference between the flanges of
440mm, the water column pressure will be
0 - 440mm wc.
LRV = 0.0 mm wc
URV = 440 mm wc
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
What is transducer
What is Integral and Derivative control?
why 4 to 20 ma used at 0 set
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
what is loop1 and loop2 in MTS LT?
what is skin type thermocouple? how it is installed? what is the difference b/w thermocouple & skin type thermocouple? what is gounded & non-grounded thermocoplle? what is the diff b/w these two?
2 Answers KazStroy Engineering, PSU,
Transmitter reading is zero but in DCS showing one Bar what is the reason ?
How does one detrmine the direction of movement of core in an LVDT?
why Fahrenheit unit of moistur analyzer transmitter
Guy's need your support,I want to measure closed tank level which is under vacuum -630mmHg using DP Transmitter, tank fluid density 1.38, Tank height is 7ft
I have a steam flow DP transmitter that has output swinging. Steam valve is in manual.I have good steam pressure. The impulse lines have steam tracing on them. The steam tracing has a hole in it that is blowing raw steam on the high side impulse line only. Could this be causing the swinging?
Sitrans LR460 Radar level transmitter getting level out or disturbed level during moisture present in the material ie coal in the pccb bunker in CHP.Any suggestions for this problem...????
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)