Can DP transmitter with orifice plate works on Beta ratio
0f 0.3 and differential pressure of 100 MMWC in liquid
service application?
Answer / carl_ellis
An orifice plate (OP) creates a pressure drop in the flow
stream.
The question is whether an orifice plate 'works'. Works how?
An orifice plate will always 'work' by creating a pressure
drop; the proper questions are whether the permanent
pressure loss is excessive, whether the orifice plate has
been 'sized' for a specific medium at correct design
conditions, and whether the pressure drop (DP) is adequate
for instrumentation that senses the DP.
Orifice plates typically drop 100 inches water column at
100% flow rate, about 25 times the DP of 100mm water column.
A DP of 100mm water column at 100% flow rate is more
typical of an averaging pitot tube than an orifice plate. A
full scale flow rate of 100mm w.c. requires a low range
pressure transmitter, or one with a high turndown ratio.
A 0.3 Beta is acceptable.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
how will do square root transmitter calibration
Coal mill Instruments Equipments for cement plant And process diagram ?
explain Cascade Control strategy with the help of a block diagram. also exlain its working in a distillation column
Explain the difference between the types of input variables plc?
what is sliding spool valves?
how to check earthing,what is minum ohms for proper earthing
How will you calibrate an interface level trol/normal level trol in line and in w/s?
describe flow nozzel principle?
Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plants instrumentation field , which one field is give long life & which one field is best ,I confused a lot And also I'm studying AMIE, can I choose which field from Section B examination?
What FLOW METER generally used in Gas plant?
How to calibrate the control valve.
how to calibrate transmitter online (in running plant)please explain correct procedure