What is the max demand on your transformer and your company?
Answers were Sorted based on User's Feedback
Answer / jatinder dhaliwal
max demand of a company and transformer is the maximum
power that his circuit is likely to draw at any time.
Is This Answer Correct ? | 54 Yes | 4 No |
Answer / mohd. karim
i want to give answer of this que. by an Example:
**if connected load of our system( factory,
Works,plant ...Etc) is 1250KW(1.25MW)...it means our maxi
demand at PF 0.83 is 1506KVA (1.506MVA)
one transformer used for this load with rating PF 0.8,
11kv/0.415, 1500kva
***it means MD in KW is 1200KW
MD in Kva is 1500KVA (1.5MVA)
it means this x-mer is not suitable for this load because
efficiency of x-mer is maxi. at half load. for above
example, this x-mer is suitable for 600KW-850KW at
PF=0.83)
Here
** is the MD of Company
***is the MD of X-mer
Is This Answer Correct ? | 25 Yes | 5 No |
Answer / pablo
The maximum demand of a power transdormer does not exceed
80 percent of its power rating.
Is This Answer Correct ? | 18 Yes | 6 No |
Answer / sp singh
Transformer generally selected 25% higher KVA than peak load of the organization.
Is This Answer Correct ? | 4 Yes | 0 No |
Maximum Demand (kVA) is your peak demand of electricity from the grid. ... Your energy distribution company charges you for the maximum demand, so it costs you money. Maximum demand (MD) is the peak level of electricity demand recorded by TNB meter during a 30-minute interval in a month. The amount charged to a user is based on the recorded MD in kilowatt (kW) multiplied by the respective MD rate.
Company MD is sanctioned MD which you have to maintain to avoid penalty from Electricity Board
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naveenkumar m
The recorded maxdemand is the maximum demand of transformer
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / will
Maximum demand means that it shall not cross the 100%
rating of the transformer, if the transformer has no
colling stages and can take extra demand.
Normally the cooling stages increase the transformer
capacity to take load 33% more at eact cooling stage.
Ist cooling stage FA-1.33%
2nd cooling stage FA-1.66%
That means when the transformer getting loaded more than
100% capacity the ist cooling stage gets automatically on
and when it gets more than 133% loaded the second cooling
stage gets automatically on.
Is This Answer Correct ? | 4 Yes | 11 No |
Answer / stanley electrician
Consider that 500kva transformer in your company,
and you use only 250 kva load maximum. you must calculate
the increase of your load for the future five years.
That means, expecting 275 kva load in feuture, you will get
upto 300 kvaon maximum demand.
Simply get 25% extra from the maximum load.
Is This Answer Correct ? | 5 Yes | 13 No |
1.what is electricity 2.what is electronice 3.how many modules 4.five electrical component with symbol 5.five electronice componene with symbol 6.how convert 220v.A/C to 24v/DC 7.220V.WAIRING DIAGRAM OF AMMETER/VOLTMETER/OHMMETEER
if field current decreases how can the speed increase in the unloaded dc series motor
Difference between a pilot wire and a normal conductor?
0 Answers United Arab Aluminum Company,
WHERE IS THE LIGHTING ARRESTER SHOULD BE PLACED IN DISTRIBUTION LINES?
What should be the earthing resistance of an industrial substation and also What should be the house hold earthing resistance?
20 Answers Jindal, Pharma, TAAT, TATA,
hopkinson's test
what is the star delta connetion and how can do it a three phase motor with control witing with picture
0 Answers Aurobindo, SA Kent, Wipro,
we specify current in case of feeder but in case of distributor voltage, why?
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
why there is a phase difference between line voltage & phase voltage ?
What happens when DC supply is given to transformer
What is evaporator & condencer & compressor