How to convert 0-2500mmH2o into kg/hr?
Or how to convert mmH2O into kg/hr,t/hr etc
Answers were Sorted based on User's Feedback
mmH2O is units of pressure, probably differential pressure in a case involving flow rate.
kg/hr is units of mass flow rate, kilograms per hour.
There is no inherent or implicit relationship between mmH2O and kg/hr. Therefore, there is no conversion between the two.
Differential pressure can be used to measure volumetric flow rate of liquids and gases and an inferred mass flow rate can be calculated for liquids with a known density and gases when there is static pressure and temperature compensation.
But not only do those those measuring conditions need to be met, but DP flow rate is dependent on a specific differential primary flow element and the characteristics of the fluid involved.
That means a measurement in mmH2O pressure drop in a specific design for a liquid differential flow meter could might be converted to a kg/hr mass flow rate (with appropriate static pressure and temperature for gas), but it would be specific only for that application and not transferable to any other application.
Any given DP measurement, say 2000 mmH2O, can represent 1.20Kg/hr in one flow meter and 45,000kg/hr in another flow meter. There is NO inherent relationship. Any correlation is application-specific.
| Is This Answer Correct ? | 24 Yes | 3 No |
what is the difference between signal cable and ontrol cable?
hello this is dhinakar subramanian. how to piping and instrumenation drawings and also how to create the data sheets...
Explain Three way boiler.
I am a electronics and instrumentation fresher trying for a job in IT sector. what do need to prepare for the interview?
What are the different types of thermistors used in industries? How to the operation of typical thermistor?
What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process
What is the expansion of RADAR? How it works?
what is the basic working principle of I/P and Positioner in any control valve.
In control valve proximity inductive sensor is taken as digital feedback for full open and full close.Normally its volts 24v when the sensor acts the feed back voltage 14v so that our relay not indicating in plc panel . kindly give the solution.
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
What is scan time of PLC?
what is thermopile?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)