How to convert 0-2500mmH2o into kg/hr?
Or how to convert mmH2O into kg/hr,t/hr etc
Answers were Sorted based on User's Feedback
mmH2O is units of pressure, probably differential pressure in a case involving flow rate.
kg/hr is units of mass flow rate, kilograms per hour.
There is no inherent or implicit relationship between mmH2O and kg/hr. Therefore, there is no conversion between the two.
Differential pressure can be used to measure volumetric flow rate of liquids and gases and an inferred mass flow rate can be calculated for liquids with a known density and gases when there is static pressure and temperature compensation.
But not only do those those measuring conditions need to be met, but DP flow rate is dependent on a specific differential primary flow element and the characteristics of the fluid involved.
That means a measurement in mmH2O pressure drop in a specific design for a liquid differential flow meter could might be converted to a kg/hr mass flow rate (with appropriate static pressure and temperature for gas), but it would be specific only for that application and not transferable to any other application.
Any given DP measurement, say 2000 mmH2O, can represent 1.20Kg/hr in one flow meter and 45,000kg/hr in another flow meter. There is NO inherent relationship. Any correlation is application-specific.
| Is This Answer Correct ? | 24 Yes | 3 No |
you are on site,the plant trips,you are approached by operations,what do you do?
Explain any simple temperature control system.
How can I zero check of wet leg type DP Tx ?
What is the working principle of oxygen analyzers(zirconium oxide type) used in CFBC boilers?
3 Answers Bajaj, Kohinoor, Wartsila,
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.
why to use 3 wire at RTD ? what's the reason for common wire ?
How can we test a bently nevda 3500/42M accelerometer monitor card by simulating it with test equipment?. what king od of signal (milli volts or volts or or resistance ) we should feed in the terminals of the card?
What is difference between differential pressure & delta pressure?
why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?
i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)