Why only negative 24 vdc supply give in vibration measuring
system.
Answers were Sorted based on User's Feedback
Answer / nandan
The principle is that analyzer supplies a negative voltage
to transducer,who converts it into a frequency & sends it
across the probe.Now as the probe comes into the area of
rotor it creates a magnetic field & with it eddy current is
produced on the rotor side.Which changes the amplitude of
the frequency.It induces the voltage & remaining frequency
comes to the transducer through the return way.Transducer
converts it into the voltage .
Now coming back to the question The gap voltage has a
negative relation with the voltage induced i.e. as the gap
increases the induced voltage decreases.So to make it to
into a linear relation ship, negative voltage is supplied.
i.e
Gap Gap voltage
0 mm 0 vtg
1 mm -9 voltage
2 mm 18 voltage
& when the probe is in air it will have no induced voltage
so all -24 voltage without induced voltage will return back.
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / jigaranadkat
Because it has PNP transistor inside which requires base
bias of negative (-ve) supply.
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / darpan
The principle is that analyzer supplies a negative voltage
to transducer,who converts it into a frequency & sends it
across the probe.Now as the probe comes into the area of
rotor it creates a magnetic field & with it eddy current is
produced on the rotor side.Which changes the amplitude of
the frequency.It induces the voltage & remaining frequency
comes to the transducer through the return way.Transducer
converts it into the voltage .
Now coming back to the question The gap voltage has a
negative relation with the voltage induced i.e. as the gap
increases the induced voltage decreases.So to make it to
into a linear relation ship, negative voltage is supplied.
i.e
Gap Gap voltage
0 mm 0 vtg
1 mm -9 voltage
2 mm 18 voltage
& when the probe is in air it will have no induced voltage
so all -24 voltage without induced voltage will return bac
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mohammed abbas
Because it is NPN tansistor during the initail days when
this was inveted by bently the cost of NPN transiator was
less. then they started use NPN transiator for the
vibration propbe, due to this we will give negative 24vdc
supply
| Is This Answer Correct ? | 5 Yes | 7 No |
Answer / sai kiran.c
does really negative voltage exists......???
| Is This Answer Correct ? | 0 Yes | 5 No |
1- Explain about HPM 2- What is the FSC and explain the configuration of FSC 3- explain the complete loop of vibration, how it works (field to control room) 4- What is the use of proxymitter? 5- During job your partner effected with H2S then what you have to do. 6- what type of gland packing uses when valve glind is leaking.
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
how to calculate static pressure in a pipe line,when we know the DP(differential pressure) in the line, area of the pipe? please any one tell me the relation between them..?
how to install the Ph and Conductivity analyser? is there are any procedures which has to be maintained.
What is the formula to convert mv to temperature in k type thermocouple?pls simply elaborate? I got one ans.it is Temp=mv×25°+atmospheric temp,but here what is 25°,i confusef ,so pls????
Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?
Dear Sir/Madam, I am attending an interview for ETs in BHEL. I have cleared my written test under Electronics (Instrumentation). This is the first time I am appearing for an interview. Can any one who has attended the interview earlier give me a clue to face the interview. With regards Sindhu
what is the difference between laminor flow and turbulant flow
how to calibate level transmiter ?range -150 to +150.what is the zero and span?
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
what is Pre- commissioning.
I saw one P&ID 6" control valve has been connected with 8" process line, and 2" valve also connected in parallel with 6" valve. why the 2" valve connected in parallel, Is there any technical reason. please clarify. With Regards-Kittu
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)