while we select CT, why the CT ratio is divided by 5??
ex:250/5,15VA,CLASS-1 CT.Why it is divided by 5??Help me please
Answers were Sorted based on User's Feedback
Answer / dinesh
CT has primary and secondary, Normally in industries most
of line cable is reffered as primary and your CT coil is
secondary. if you have a CT of 250/5 that means when there
will be a flow of 250A current in your primary side then
you will obtain 5A current on secondary side. Now if you
divide 250 by 5 you will get the CT ratio that is 50. now
if you obtain 3A in secondary that menas 3A mutiply by CT
ratio That is 50 you will get 150A flowing through primary.
your CT is used for protection as well as metering purpose.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / velappan
it is not divided by 5
the primary current is 250A and secondary current is 5A in this case and 15VA is burden we connected on secondary
Is This Answer Correct ? | 0 Yes | 0 No |
in our transmisison sub station why we step down firstly 132kv\33kv then 33kv to 11kv. can we direct step down 132kv to 11kv.
Find defination of KVA convert in to KW.
HOW can i REuse the fused MLL LAMPS & GLS LAMPS at our factory
How does the slip regulator works as a startor
how to estimate wiring ins roughing ins. and boxes
If i am running of spindle at 2000rpm ,but How to spindle stop at the second I am resetting the machine in CNC machines
On the secondary side of a distribution transformer, we use 1c x 630 sq mm cable. Why dont we use 4 core cables instead of 1 core cables on the secondary. Why we use aluminium cable glands on the outgoing instead of brass cable glands?
Difference between field rheostat and armature rheostat.
ARE YOU NOURVAS ?
where reactive power is used
Motor also having losses, we call KW rating. In transformer and generator having losses but we call KVA Rating why?