while we select CT, why the CT ratio is divided by 5??
ex:250/5,15VA,CLASS-1 CT.Why it is divided by 5??Help me please
Answers were Sorted based on User's Feedback
Answer / dinesh
CT has primary and secondary, Normally in industries most
of line cable is reffered as primary and your CT coil is
secondary. if you have a CT of 250/5 that means when there
will be a flow of 250A current in your primary side then
you will obtain 5A current on secondary side. Now if you
divide 250 by 5 you will get the CT ratio that is 50. now
if you obtain 3A in secondary that menas 3A mutiply by CT
ratio That is 50 you will get 150A flowing through primary.
your CT is used for protection as well as metering purpose.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / velappan
it is not divided by 5
the primary current is 250A and secondary current is 5A in this case and 15VA is burden we connected on secondary
| Is This Answer Correct ? | 0 Yes | 0 No |
We've 2 diffrent DG's with same capacity (500 KVA). Can we sync them ?
Why not connect relay Y phase for over current and earth fault
How much minimum insulation required between 11kv/3.3kv transformer windings?
WHAT IS MVA RATING OF KOTHAGUDAM THERMAL STATION POWER TRANSFORMER?
I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. earthings are connected to T/F body, and 02nos. earthings are connected to T/F neutral.T/F capacity is 2000KVA, 11KV/415V. But after completing of 02 years successful operation ,we are facing following problems- 1. CT/PT occured blast one time 2. HT cable box occured blast two times 3. One body earthing strip and one neutral earthing strip of transformer are overlapping at some places. Whenever these two strips are pressed at overlapped points, they made spark. What is the reason of spark? Please explain the reason & rectification of above problems
Hi, what is 100 % stator earth fault protection and how it can be achieve by 3rd harmonics and low frequency injection principle ?
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
25 kva load,
How to calculate the average power factor in 3 phase unbalanced system
specify the inbuilt protections in DG
What is steady state response?
1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)