Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


when the motor was star position that is running ok but when
the motor was delta it was tripped? why?

Answers were Sorted based on User's Feedback



when the motor was star position that is running ok but when the motor was delta it was tripped? wh..

Answer / pawanchauhan12

basically this type of problem created when motor winding delta coil sequence not proper. For finding of fault following this processor :- Firstly check motor winding continuity 1:5{RR} ,2:6{YY} & 4:3{BB} .if continuity not matched then interchanged sequence of {RR} wire of power .if problem not solved then again interchanged second sequence of {YY} wire of cable .

Is This Answer Correct ?    5 Yes 2 No

when the motor was star position that is running ok but when the motor was delta it was tripped? wh..

Answer / pramit dutta

By connecting the stator winding 1st in star and then in delta
,the line current drawn by motor at starting is reduced to 1/3 th as compared to starting current with the windings connected in delta.

Is This Answer Correct ?    3 Yes 1 No

when the motor was star position that is running ok but when the motor was delta it was tripped? wh..

Answer / santosh kumar kishore

in delta connection motor takes more current and in star
position motor takes less current so either change
connection or increase relay setting.

Is This Answer Correct ?    2 Yes 2 No

when the motor was star position that is running ok but when the motor was delta it was tripped? wh..

Answer / a p patil

motor star connection join winding terminal C2,A2

Is This Answer Correct ?    0 Yes 0 No

when the motor was star position that is running ok but when the motor was delta it was tripped? wh..

Answer / naveen joshi

There are many reason whether resistance increased by terminal contact in motor or phase difference in roter and stator not matched during transition from star to delta , increase the pause timing in timer .
.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.

0 Answers  


we have an energy meter in a capacitor bank panel, So should we consider it's readings as energy consumption on daily basis. (when capacitor bank doesn't have any energy losses)

0 Answers   Honda,


Which type of transformer is used for lighting loads?

0 Answers  


why capacitor burst?

2 Answers  


what does happen if generator frequency fall in running condition & what should require immediately

4 Answers  


What is different bewteen low or high impedance busbar protection scheme

0 Answers  


how to calculate 3 phase clearance in Tower line , 33& 11 KV Line and LT Line.

1 Answers  


WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?

5 Answers  


Can anybody explain Why starters are not used for motor starting in industries?

9 Answers  


In vapour absorption refrigeration machine fluids used are

0 Answers   Caterpillar,


can anybody tell me that for p.f. Improvment we use capacitor banks but how to decide its capacitance. As we all know how to calculate kvar but what abt capacitance value

0 Answers  


How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)