when the motor was star position that is running ok but when
the motor was delta it was tripped? why?
Answers were Sorted based on User's Feedback
Answer / pawanchauhan12
basically this type of problem created when motor winding delta coil sequence not proper. For finding of fault following this processor :- Firstly check motor winding continuity 1:5{RR} ,2:6{YY} & 4:3{BB} .if continuity not matched then interchanged sequence of {RR} wire of power .if problem not solved then again interchanged second sequence of {YY} wire of cable .
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / pramit dutta
By connecting the stator winding 1st in star and then in delta
,the line current drawn by motor at starting is reduced to 1/3 th as compared to starting current with the windings connected in delta.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / santosh kumar kishore
in delta connection motor takes more current and in star
position motor takes less current so either change
connection or increase relay setting.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / a p patil
motor star connection join winding terminal C2,A2
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naveen joshi
There are many reason whether resistance increased by terminal contact in motor or phase difference in roter and stator not matched during transition from star to delta , increase the pause timing in timer .
.
| Is This Answer Correct ? | 0 Yes | 0 No |
Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.
we have an energy meter in a capacitor bank panel, So should we consider it's readings as energy consumption on daily basis. (when capacitor bank doesn't have any energy losses)
Which type of transformer is used for lighting loads?
why capacitor burst?
what does happen if generator frequency fall in running condition & what should require immediately
What is different bewteen low or high impedance busbar protection scheme
how to calculate 3 phase clearance in Tower line , 33& 11 KV Line and LT Line.
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
Can anybody explain Why starters are not used for motor starting in industries?
In vapour absorption refrigeration machine fluids used are
can anybody tell me that for p.f. Improvment we use capacitor banks but how to decide its capacitance. As we all know how to calculate kvar but what abt capacitance value
How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)