Can anybody explain Why starters are not used for motor
starting in industries?
Answers were Sorted based on User's Feedback
starters are used in industries ,i have seen thousands of
motors starting through starters. you have to use
starter ,its type may change like dol,star-delta,soft-
starter,oil-starter,ats.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / pillay
Is your question correct? All motors must be started with some
type of starters what more if they are used for industrial
purpose.
In addition to provide a safe mean of starting and stopping
the motor it should be able to to protect the motor itself.
With the help of a starter you can provide overcurrent and earthfault protection unauthorised starting unwanted stopping
and you can plan your starting and stopping as desired.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sreenu
As per IE rule, we must use starter for morethan 3KW
motor.So please use starter, otherwise your motor may
burntout due to high starting current.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / modi.elect2002
In industries starters are used widely. I have seen thousands of starters.
most common types are DOL, Star-delta, Soft starter.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / habib
Actually In Industries Every Machine connected to motor
is to be respond as early as posible i.e with in
milliseconds,If u use starter motor has take some time to
take full load.
Is This Answer Correct ? | 1 Yes | 8 No |
starer reduce starting current with adding the external
resistance with the armature in series ,because the
resistance of the armature is very less,so starting current
is very high .
I=V/R if r is less then curent is very high
to reduce the starting curent starter is used.
up to 5 hp motor dol starter is used
but in industries the rating of the motor is if higher
thane 5 hp then starter is not used
Is This Answer Correct ? | 1 Yes | 9 No |
why in three phase 440 circuit in all phase current is almost equal L1-35 A,L2-34 A ,L3-31 A but in nutral when i check with clamp meter it shows 25 A?
how solar power plant energy meter multiplication factor
For a certain load i need 100kw load ,In that case what rating mccb should i use?
how many types of accuracy class in ct? what is meaning of 5p20?
whats the application of voltage regulation? and whats the voltage regulation's device?
can we synchronize star system generators with delta system generators?
How out of step protection relay works?
What is the impedence of Transformer?
factor to be considered for bus bar design
What is the definition of ohms law?
7 Answers AZ Engineering, Ecil,
sir, What is the purpose in Generating power plant is operated Lagging PF and Above 0.9 lag PF?
I have a 25kVA three phase transformer on our property. Will this transformer be large enough to run a large home with swimming pool, spa, 2 off full size reverse cycle air conditioners to service a 100 square house (10,000 square feet or 930 square metres)and the general power consumption of this house without upgrading to a 63kVA transformer.