what does happen if generator frequency fall in running
condition & what should require immediately
Answers were Sorted based on User's Feedback
Answer / kailash
Either we have to reduce load or we have to increase speed
of prime mover by increasing fuel (diesel/steam) through
governor.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / poorna
if the generator frequency falls during running condition
it may result in circulating currents if it running in
parallel with other generators or it is connected to grid,
remedy is to increase the speed of prime mover by any means
if not possible reduce the load
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / siva rao
the emf induced in alternator will reduced to very low value
and the generator will not serve any load.if the frequency
will fall to a lower value the excitation of the generator
must be increased.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mahi&junu
there are two methods. Either we can decrease the load connected or we can increase the excitation
Is This Answer Correct ? | 5 Yes | 3 No |
What is the formula for calculating the Instantaneous Short Circuit & overcurrent for any breaker
1 KVAR = 1.3Amps but, 25KVAR capacitor/690V capacitor takes just 21Amps as leading current, what is the reason? Please explain...
how many mega ohms insullation of the cable can't be use when testing with megger tester for Low voltage cable 240V use?
I am an American living in Vietnam and I have recently gotten a refrigerator from Japan and it is rated for 100 vac, but the power here is 220 so I bought a voltage stabilizer it has a 1 kva output rating. Can you please tell me what the amperage is? I'm confused and without a working fridge.
Type of motor stater detail and working detail
what is the isolation transformer. what is the isolator?
what is the function of garing capacitir in SF6 circuit braker?
What test must you do before powering up a circuit that you have been working on?
Can any body tell me what is use of END OF LINE RESISTOR in fire alaram circuit?
Why there is a current in neutral line
What is the need of ISOLATION Transformer?
why do the core of transformer saturates???