We use ACB in LT and VCB in HT.But if we use VCB in LT and
ACB in HT that what will be the effect on the system or any
power range?
Answers were Sorted based on User's Feedback
Answer / jithin
VCB is designed for HT it has vaccum chamber that prevents arcing and it triping speed is higher
ACB is desined for LT the terminals are almost open to atmospere it can cause flashing if we use it on HT
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / karna
HT Line Means 6.6KV,11KV and 33KV. LT Line means 415V. So
the ACB are Manufacutered for LT side because , based on
shortcircuit KA busbar terminal are designed in ACB . In HT
line while switching On & OFF ARC will be more it will not
withstand in ACB . IF we use VCB in LT side , the VCB will
not helpfull at fault condition, because its upstream
breaker will trip or component will damage
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / maurilio
if you use a VCB in low tension it odes not make problems
but if a ACB or Air Circuit Breakers in HT you will see a
lot of ligthning and probably fire in the breaker
So it is no convenient to use a ACB on HT
| Is This Answer Correct ? | 13 Yes | 8 No |
Answer / sushil kumar
Vcb is ht supply use rating of high voltage but acb lt supply used this manufacture 440 voltage difference for relay siting vcb and acb vcb is use closed area but acb use open area
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hardik
As per Karna ACB is not usfull in HT because of its limited
capacity but in casw of VCB apply in LT it can dafinatly
helping out after making its ragular reliese setting and
tripping in foulty condition is depend on relay... so VCB
we can use but drow back is VCB in LT system it is more
expancive then ACB thats it...
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / kishore
actually acb is made for LT bcz EVERYTHING HAVE A LIMIT,SIMILARLY IF WE USE VCB AT LT THEN NO PRBL BUT IT IS A GREAT ECONOMIC LOSSES FOR US OK.
| Is This Answer Correct ? | 2 Yes | 3 No |
mccb service sittings be done?
how to reduce disel generator voltage from 410-60 hz to 380v-60hz
Is it mandatory statutory requirement of transformer oil filtration annualy despite oil is withstanding required dieelectrical strenth and all others parameters
now a shunt motor is practically a constant speed motor , then how does it meet the increase or decrease in the load ?
WHAT IS THE USE OF PIG TAIL IN WINDOW CT ?
diesel generator not getting start so whats problems will happen to DG and how we can start DG
when we see the lube oil grade its 15w/40 or 20w/40 in this what is W Explain breifly
The company is wiling to buy you 5 pcs of equipments in your electrical tool kit. Plz tell what are the 5 things you want?
What is 2P*0.5 sqmm screened copper cable and what is the use of it..?
What is Automatic Voltage regulator(AVR)?
what is the disadvantage if earth is connected to neutral
We are dealer in Maharashtra State & We have recd. form C from dealer of Maharashtra State against our E-1 form. Now assessing authority is asking for counterfoil of our E-1 form. But, our E-1 form counterfoil is misplaced somewhere & assessing authority is disallowing the C form which is recd. from Maharashtra State.Please let us know the option for allowing C form?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)