A 30KW motor running at 1450 rpm draws 56A, how would you
determine if this is correct or not?
Answers were Sorted based on User's Feedback
Answer / divakaran a
P=1.732xVxIxP.F
30KW=1.732x415xIx0.8
I=30000/(1.732x415x0.8)
I=52.17 AMPS
sO the current drawing from the motor is 52 amps (Theoriticaly)
in practical the motor may draws more current as based on the load.
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / vipul kumar rai
P=1.732xVoltage x I(current )xPower Factor
30KW=1.732x415xIx0.8
I=30000/(1.732x415x0.8)
I=52.17 AMPS
as per thory 52.17A current draw.
so 56A is approx correct.
Is This Answer Correct ? | 2 Yes | 0 No |
What is the use of bundle conductors?
If one ct is reversely connected in Y system what will effect in kwh and kvarh meter?
advantage of cu cable over al cable
What is VCB? Where it is installed?
how to copy from plc ge fanuc versamax series,all input and output, adress, and printout.
what work will do diffrential realay DG set
0 Answers IG Petrochemicals Ltd,
WHY PROTECTION CT IS USED NEXT TO METERING CT?
what are the installation procedure of high voltage power transformer,CT,CB&PT?
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS?
I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?
If i connect aload to phase taken from one transformer and neutral from another what will happen.
what do u understand from filter factor of reactor?