What are the turbine protections.
Answers were Sorted based on User's Feedback
Answer / jerry smith
Gas and Steam Turbine Basic protection include:
Overspeed, high vibration, Low lube oil pressure, and high
lube oil temperature.
Specific to gas turbine would be high exhaust temp, excess
spread of temperatures in the exhaust, inlet suction low
pressure, combustion pulsations, compressor bleed valve not
closed, underspeed too close to surge point, fuel valve not
in proper relation to turbine load, and flame detector
failure.
Specific to steam turbines would be inlet steam temperature
high or low, inlet steam pressure low, exhaust steam
pressure high, exhaust steam temperature high, drum level
high on the supply boiler.
Generator faults do not always trip the associated Turbine.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / kaizad
Turbine protection in steam turbines are mainly overspeed, low steam pressure, low vacuum, low vacuum backup, exhaust hood high temperature, loss of generator seal oil, stator water temperature hi, gas concentration very high in stator water,manual trip & electrical trips associated with generator, main transformer, unit service transformer
| Is This Answer Correct ? | 6 Yes | 0 No |
What is the the sequence/logic of burner management system in boilers. What is purging and scavenging?
im try to calculating seawater flow required for SW-FGD system. I need a guide, equation or method to do it, can some one help me! Thanks very much
what is the formula for converting mmwc to tph in a dp type transmitter.what is the range in plc(in tph) if dp tx.range from 0 to 5000mmwc.
2 Answers CCC, Korba Power Plant, Shyam Steel, Utkal Alumina International,
How do you consider that you can improve and what assistance do you need to achieve this
1. what is meant by burner tilting?
I am opertaing generators which are beyond 14000hrs and now the fuel consumption is about 2kw per liter of diesel. The engines are due for overhauling. is this normal
whats plant?
63.5 ohm NGR is connected with our gas engine genrator running at 500 rpm, 50 hz and synched with WAPDA at 6.3 KV bus voltages, 2500A and 25KA(1 sec). can some one give me proper calculations how it comes 63.5ohm?????
under which situation or why restricted earth fault protection operates in out side its zone that is external fault
Where is the pressure reduce valve in the power plant
what is the meaning of SST300 V56A in SIEMENS turbine
can dp type level transmitter work in under vaccum condition
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)