what is the relation between the grid voltage and generator
voltage how to link up generator with grid
Answers were Sorted based on User's Feedback
Answer / muili ibrahim babatunde
This involves synchronization process. Hence, For the two voltages to link, these parameters must be met:
(1)Frequency ( Hz ) : The frequency of the voltages produced by the generator must be equal to grid voltages
frequency.
(2)Voltage ( Volt ) : The line voltages produced by the generator must be equal to the grid line voltages.
(3)Phase Sequence : The phase sequence of the voltages produced by the generator must be same at that of the grid.
(4)phase angle : The phase angle of voltages produced by the generator must be the same with that of grid voltages phase angle. (5) The waveform of the voltages produced by the generator must be the same with that of grid voltage.
| Is This Answer Correct ? | 8 Yes | 0 No |
It is better to have generator voltage slightly higher ( not exceeding 3 %) than grid voltage ,while synchronizing , to avoid leading pf on synchronization
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / abhilash
After satisfying x7 criteria......our required parameters (v,phase sequence,p angle,hz and etc )will achieve.......if any in this is not achieved we cannot approach with the grid........thank you
| Is This Answer Correct ? | 0 Yes | 0 No |
why the Steam Turbine(20MW)center line and gear box center line not in same elevation during coupling alignment ?
3 Answers Greenesol Power Systems,
why drum level falls when one of the running coal elevations tripped?
what is under voltage protection 27
what is the condition of transformer parallel operation ?
We know primary ,secondary air so, What is the work of Tertiary air in Thermal power plant
Due to the sensitive earth fault Our Power plant Get Tripped Several Times, It happens in the morning time daily, When temperature rises that means sun rises the earth fault current get lower, in this situation What should I do to get rid of this Problem?
What is indipendant power plant
What should be the neutral and body grounding sysytem for grid (132 KV) parallel generators (440 volts)?
What is tripping relation between the turbine exhaust pressure and turbine last stage pressure....???
What is droop.
2 Answers Dhampur Sugar Mills, Elaf,
63.5 ohm NGR is connected with our gas engine genrator running at 500 rpm, 50 hz and synched with WAPDA at 6.3 KV bus voltages, 2500A and 25KA(1 sec). can some one give me proper calculations how it comes 63.5ohm?????
how mony power plants in India
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)