please explain clearly in PID controller if We increase P
only what will be action of the contrlere.
Answer / carl_ellis
Any given amount of error will produce less output change
than before the proportional band was increased.
Increasing the proportional band will make the controller
less sensitive to the deviation of the process variable
(PV) from the setpoint (SP).
Tell 'em Carl sent you.
Is This Answer Correct ? | 2 Yes | 4 No |
I heard that we can use flow transmitter for level measurment also hw it is?
tell me the field & lab calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter, temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue),
Why using negative voltage in vibration measurement?
in a power plant which system are compensated?
What is calibration?
Thermocouple is a transducer but rtd is not transducer why? Both taking heat as a input and giving mv
What are primary elements of measuring pressure? Which type of pressure can be measured by these elements?
Advantages of servers over normal desktop in PLC SCADA system
principle of automatic votage regulator
POSSITIVE PULSE IS APPLIED TO AN INVERTER INPUT.THE TIME FROM THE LEADING EDGE OF THE INPUT TO THE LEADING EDGE OF THE OUTPUT IS 10 ns. THE TIME FROM THE TRAILING EDGE OF THE INPUT TO THE TRYLING EDGE OF THE OUTPUT IS 8 ns. WHAT ARE THE VALUES OF tPLH and tPHL?
which are types of orifice tap ?
Can Any body tell me how to check Modbus Settings in ER300N L&T trivector meter?