To find closed tank level by DP transmitter , how to
findout its range.and insomeplace they using range like -
1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit
they range for minus and plus.and why?
Answer / yashwant
THIS IS LEVEL MEASUREMENT USING DP TRANSMITTER, CLOSE TANK
MEANS PRESSURIZED ,PRESSURE IS EVERY WHERE IN SIDE TANK WILL
BE SAME. LOW SIDE WILL BE TOP SIDE WHERE ALL CONDENSATE
COLLECTED THIS IS REFERENCE SIDE, NOW ON OTHER HAND HIGH
SIDE WILL BE LOWER, DIFFERENTIAL PRESSURE OBSERVED AT DPT.
LOWER SIDE WILL BE ALWAYS FULL IE FULL SCALE IF YOU ARE
HAVING TANK HEIGHT 1500 MM THEN PRESSURE AT LOWER SIDE IS
1500 MMWC. AND THAT OF HIGHER SIDE WILL BE THE ACTUAL WATER
INSIDE TANK WE SAY 500 MMWC STEAM PRESSURE WILL BE EVERY
WHERE SAME SO NO NEED TO CONSIDER PRESSURE INSIDE THE TANK.
MINUS AND PLUS WILL BE JUST FOR HAVING DIFFERENCE IN TWO
COLUMN IE HP AND LP. ALSO TANK IS NOT PRESSURIZED YOU CAN
USE PRESSURE TRANSMITTER CALIBRATED IN YOUR RANGE (HEIGHT OF
TANK MMWC)
Is This Answer Correct ? | 6 Yes | 4 No |
how to convert % to ma
1 Answers Flour Tech Engineers (P) Ltd, Techint,
How flow can be measured with dp?
If we interchange HP and LP tapping in drum level measurement and reverse LRV & URV correspondingly.What is the difference between the normal tapping(HP,LP) and reversed tapping(LP,HP)?
why do we use 4-20 ma current why cant o-20ma
what is the difference in Kg/cm2 and mmwc?
you are on site,the plant trips,you are approached by operations,what do you do?
What is the PLC Level & type.
2 Answers Bhushan Power Steel,
How to calibrate the magnetic flow meter and how to correct the flow if it is showing more flow.
5 Answers Bohra Industries Limited, TCL,
What are difference between automatic and manual control system?
What is the advantage of using locally fabricated hook ups over Pre fabricated hook ups in process instrumentation?
0 Answers Engineers India Limited,
thermocouple output is AC OR DC??
What is the relationship between GAIN and PROPORTIONAL BAND.
1 Answers Kharafi National, Sabic,