SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN
THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE
CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS
BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I
REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT
STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS
INITILAZIATION PLEASE HELP ME READRING THIS?
Answers were Sorted based on User's Feedback
Answer / warren emmett
Firstly, you should use a loop simulator and simulate the
Milliamp range to the dcs 0 to 20 or 4 to 20 do this in 25%
steps.If the dcs responds to the signal then the problem is
with the radar transmitter. If the problem persists when
simulating the the problem is on the Input card. Could be a
zero volt issue, a faulty input card or a wiring issue
could even be software related. To remedy the radar if that
is deemed faulty then consult the manual, you might need to
adjust parameters or do mapping of the vessel when it is
empty. Hope this helps
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / hirensinh
Set up the Parameter,Basically you know Tank is Empty or
Tank is Partially full.
Parameter set
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / prakash malviya
first u have 2 remove o/p wires of 4-20 ma then connect ma source with parellel this.then give 4& 20 ma...at 4 u see 0 %lvl & at 20 u find 100% lvl in dcs.if can't then u have 2 check from dcs side.in dcs check AI card particular channel for this.check wires grounding.
2nd condition if u find proper response in dcs with ma given to o/p wires..then go to the radar menu ..go to configuration..in that u find tank lvl...select full...then save it..
| Is This Answer Correct ? | 0 Yes | 0 No |
How works weighfeeders in cement industry? what is the working principle?
Why DP level transmitter preferred for closed vessels and Radar level transmitter for open tanks??
How to calibration of vibration probe
1 Answers Mina Al Ahmadi Refinery,
basic connection and principle of axial shift sensor n differential sensors in tubine describes n draw......
what is the way of measuring air flow in air duct?explaim instruments used and DP creation in line?
what are the three main programming languages in plc
HOW DOES SPECIFIC GRAVITY AFFECT LEVEL MEASUREMENT.
what is the procedure to callibrate temp controller ,pressure controller,etc. suppose a temp controller showing error 1.5 degree centigrate how can i minimize it.
0 Answers Sabic, Saudi Aramco Shell Refinery Company SASREF,
sir ,iam in dem urgent need of HPCL Paper of Instrumentation Branch plz send me at your earliest convenience at ujjwal_sharma1983@yahoo.com
Can we use thermocouple in generator of power station replace RTD(pt 100)? if we don't have any place for use RTD.
wHAT IS BURST MODE IN TRANSMITTER?
HI THIS IS NOOR AHMMAD.SHAIK, I AM WORKING IN INSTRUMENTATION MAINTENANCE Dept. in BOILER HOSE(BHEL HYDERABAD),,any other persons are working in same dept. i want some HELP in my subject
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)