We have 2 11kv/433v transformers for 2saperate acb for mv
panels and 1 bus coupler acb. Suppose I’ll close bus
coupler what will happen or it will be share the load.
Please suggestion and any modification required.



We have 2 11kv/433v transformers for 2saperate acb for mv panels and 1 bus coupler acb. Suppose Iâ..

Answer / satish kumar.m

Any one incomer has to be tripped according to the plc logic implemented or according to schematic / control such that only one incomer will feed entire bus with bus coupler on

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

I have calculated load for an office building which is 1200 KW as all the load is single phase therefore its 1200 kw single phase. Now i have to design Transformer and Generator for this load Please kindly give me exact answer that how much capacity of Three Phase Transformer and Three Phase Generator is required for this load.

3 Answers  


WHEN WE TOUCH THE BOTH TERMINALS OF BATTERY WHY NOT THE D.C BATTERY GIVE US SHOCK SUCH AS A.C SUPPLY?

3 Answers  


Could you measure voltage in series?

0 Answers  


Hello friends, Can anyone explain the concept of zones in Bus bar protection and how can we differentiate the main zone and check zone in Bus bar protection

1 Answers   ABB, NCC,


explain 100 percent and 95 percent earth faults

1 Answers  






what happen if one of 3-phase line has a much higher load when we are using delta to star transformer? how we can over-come from that?

2 Answers   Getco,


why we not connect the 12 V batteries in parallel to get the more backup supply for an UPS ? wheter off line or on line UPS ?

2 Answers  


can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.

1 Answers  


What are the types of earthing? Explain dagramatically.

3 Answers   Siemens,


My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help

2 Answers   Ariel,


Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?

0 Answers   Danieli,


Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)