A 11 KV motor is working. if the supplay is fail. what
will happened with it's breaker? Trip / remain the same
condition?
Answers were Sorted based on User's Feedback
Answer / nishad
The Motor will surely trip becaue by the sensing of under
voltage relay, it will give the trip command to the
breaker. once the breaker trip motor also trip. well in
cause of a small Voltage dip motor may not be trip. because
it's related to the setting of undervoltage relay.
somewhere it is set 2 second ( as per company's requirment)
if the power failure is more than set time of undervoltage
relay, motor trip
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
It will trip,if the breaker of motor has a voltage operated
hold coil which also provides protection against low voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / asish
the motor will not be tripped as there is no fault as only
supply is off.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / rajesh
as the supply power is constant, infinitely high current will flow through the circuit and hence the circuit breaker will trip.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the diffrence (Technical & Construction ) between CBCT & Normal CT?
what is meant by PU value ? anyone can you explain briefly to me ?
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5PHASE
What is the acceptable earth resistance for Commissioning the Transformer?
for 24000kv transformer what is the value earthing resistence?
In simply words(not explain any formula )what do you mean by power factor.?
Classify the different types of load.
What is the purpose of REACTOR in GIS substation?
Please brief me about number of pole in alternator.In single phase alternator coils are connected in star or series. How to calculate frequency for the same.
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
Why have to use copper cable for local isolator to motor ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)