why we take transformer reading in kva
Answers were Sorted based on User's Feedback
Answer / ajay kumar das
Transformers are rated in KVA . because it works in various PF.The P.F is vital for KW as power is V.I.PF.So as we dont know the load PF transformers are rated in KVA.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rrk
Copper loss & iron loss ,Cu Loss its depends upon current (A),Iron loss depends upon Voltage (V) ,Thats y trafo rating in KVA
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / coolclikker
because on the load end there is a real & reactive load both
are connected. Due to reactive load power factor is lagging
so due to low power factor actual capacity of the
transformer becomes less and losses increases. So that's why
capacity is always given in Apparent power(KVA). KVA is
actually the capacity that how much power a transformer can
supply to load
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / iffi
very simple the power factor of the load is unknown to manufacturer of the TRAFO. for which it is going to be used
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / karthick
The transformer will transfer both real and reactive power . That is the apparent power in KVA . That'y it is rated in KVA ,
Is This Answer Correct ? | 0 Yes | 1 No |
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
What is 100% protection of generator? Why 100% is not used but 95% is generally used?
How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.
sigal phase supply is 230 v ac two phase supply is 415 v ac why three phase supply is 415 v ac why not 690 v ac
why the making current is more than then the breaking current and if its true then its about a controling circuit or breaker power contact points
what are the different types of transformers in present? which transformer is efficient?
why m and c are shorted in wattmeter
In which of the following case, the rotating magnetic field is reversed? A regenerative breaking B plugging C dynamic breaking D forward motoring
The efficiency of a 100kva transformer is 0.98 at full load as well as half load , for this transformer what is the Copper loss at full load ?
c++ write a program to use a fuction call "max"which accepts an intger arrey of size5.as an arrument and return the larger and smallest of the arrey to main without changing. the original changing of the original position of the element of the arrey.
what is the voltage and ampere rating of all range of HT conductor?
I have a 5KVA UPS. Total load to be connected almost 3KW. Ordering a battery pack with capacity of 1920VAh. How long will the backup time be?