why we take transformer reading in kva
Answers were Sorted based on User's Feedback
Answer / ajay kumar das
Transformers are rated in KVA . because it works in various PF.The P.F is vital for KW as power is V.I.PF.So as we dont know the load PF transformers are rated in KVA.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rrk
Copper loss & iron loss ,Cu Loss its depends upon current (A),Iron loss depends upon Voltage (V) ,Thats y trafo rating in KVA
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / coolclikker
because on the load end there is a real & reactive load both
are connected. Due to reactive load power factor is lagging
so due to low power factor actual capacity of the
transformer becomes less and losses increases. So that's why
capacity is always given in Apparent power(KVA). KVA is
actually the capacity that how much power a transformer can
supply to load
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / iffi
very simple the power factor of the load is unknown to manufacturer of the TRAFO. for which it is going to be used
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / karthick
The transformer will transfer both real and reactive power . That is the apparent power in KVA . That'y it is rated in KVA ,
Is This Answer Correct ? | 0 Yes | 1 No |
Can someone explain how does an IDMT relay works.
Why do power lines not short out when they fall into water?
can we make a loop between neutral and body for grounding?
why are distributed windings generally used in alternators?
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
What are objectives of energy managements ?
why are we maintaining some specific gravity in battery ?
how to identify small motor and generator?
What will be the capcity of 3 phase DG set require for 25 KVA single phase lighting load?
The initial current is very large at the time of starting for almost all DC motors. SO WE USE STARTER FOR A SAFE STARTING but at our homes we don’t see any starters in our coolers, motors.WHY DON’T WE NEED STARTERS FOR THESE APPLIANCES?
who is invented transforner (230v).......
How we calculate the spacing between the conductors in 11,33KV lines?