what will happen if the connections of protection ct reverse?
will it burn the ct?
Answers were Sorted based on User's Feedback
Answer / sheikh
in case of reverse connection CT will not burn . however connected equipment may goes to malfunction or dead condition. as per example if Ct connected to kw meter and connection made inverse then kw meter given reading in Minus
like -245,-500kw . an other if ct work with any protection device like on reverse power relay in gen set and connection made in reverse then gen set goes on reverse power shutdown.
| Is This Answer Correct ? | 1 Yes | 0 No |
if your protection is only 50/51 there will be no effect,
but if you enable function of 32,67, and 87T, relay goes to malfuntion
| Is This Answer Correct ? | 0 Yes | 0 No |
Pl. brief about break-down maintenance of machine tool.
State nyquist stability criterion.
What is the function of wave trap in an electrical substation?
Why high Voltages come in multiple of 11, like 11 KV, 33KV, 66 KV, 132 KV etc.
How can a transformer test by megger?
Q. calculate the value of the resistor to be connected in series with a 100W; 230V lamp so that the wattage of the lamp is reduced to 35W
what is ripple component in ac supply?
WHY IN THREE PHASE CABLE 440V CURRENT FLOWS IF IN ONE PHASE 230V CURRENT FLOWS ???
two phases with neutral supply can be taken in 3C X 10 sq.mm cable .
Please give me a erda placement paper
What device is use for metering current at lt consumer end..??
what is the difference between a feeder and a cable?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)