what are the values to be accepted on 3 core 185sq mm for
11000volts on insulation resistance between conductors and
between conductors and earthed?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Normally we take 2M ohm /KV as sufficient IR
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / nikhil
1M ohms/kv + 1.
Eg: f0r 11 KV, 11+1= 12M ohms is ok.
| Is This Answer Correct ? | 1 Yes | 0 No |
A.C. withstand voltage
Wet(ph/ground)
Time duration
KV
Mins
28 KV
1 Min.
| Is This Answer Correct ? | 0 Yes | 1 No |
Give some example of fault limiting devices?
What are the testing to be done before the installation of 1000 KVA Transformer?
expansion of rccb
700KW 6.6KV slip ring induction motor to use VFD to control the speed
what are types of servo motors
what is mean by current
examples of resistive inductive and capacitive load
Can any body tell me about partial discharge test, and why it is necessary and its procedure
why abcd parameters are called transmission parameters
If we increase frequency in transmission line in lieu of voltage what will happen?
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
How to resolve if Diesel generator stop while running ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)