what will happen if the connections of protection ct reverse?
will it burn the ct?
Answer Posted / sheikh
in case of reverse connection CT will not burn . however connected equipment may goes to malfunction or dead condition. as per example if Ct connected to kw meter and connection made inverse then kw meter given reading in Minus
like -245,-500kw . an other if ct work with any protection device like on reverse power relay in gen set and connection made in reverse then gen set goes on reverse power shutdown.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
Why using synchronising methed in DG's sets?
How to work meggar?
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???
What is clock position of Transformer?what are the clock positions are there?and what is different of them?
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
what is the difference between Central Battery System and UPS in applications and uses? and why UPS suitable for Computers and central battery for emergency lighting?
what is the need to express current and voltage in rms value? rms value is also called as effective value,what is effective value?
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?
Which is the largest hydropower station in the world?
what about GD square and its important for motor design?
Is vtg is controlled by the resistor? if else how much?