1)why the transformer rating in KVA insted of KW
2)why the secondary of ct is shorted and why the PT
secondary is open
Answers were Sorted based on User's Feedback
Answer / vinod
1) The Efficiency of the transformer depends on copper
loss and core loss, prepotional to the voltage & square
ampere.also power factor is depend on load. thats why
transformer is rated in KVA.
2) CT secondary is either connected with relay/ICT or it
will be shorted as it is working as step up voltage
(dangerously high) principle, cause human/equipment damage
PT is using as a voltage measurement and
protection,winding must be open or connected with load of
rated burden.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / guest
when open circuit test of transformer we will got the iron
loss it will depends upon voltage and during short circuit
test we will got the copper loss it will depend upon
current there fore total loss in VA so we use large
capacity of transormer hencetransformer capacityis in KVA.
2)if ct secondary is open heavy emf will produced so
sarrounding equepement will burntout and CT willalso burnt
or saturated.
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / venkat
we dont know transformer manufacters the load power factor
cosumer so the trasformer rating in KVA
| Is This Answer Correct ? | 0 Yes | 2 No |
Why Transformer in KVA?
41 Answers APCPDCL, Apollo Power, College School Exams Tests, Electrical Tech, Hitech, HP, L&T, MDL, Oil and Gas Jobs, TATA,
what is the difference between switch yard to residential area.and how much required it.
What is min and max voltage between earth and neutral/phase if it perfect earthing?
37 Answers Epoch, ISS, ITC Infotech, L&T, Power Works, Statex, Sterlite, Wipro,
If R and Y terminals are short circuited,then power will cut. we all know that power cannot be stored.what will happen to already generated power at power station?
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
what is the difference b/w low voltage motors & medium voltage motors
How can calculate the efficency of the rectifier. input 240V AC, current 5 amps,P.F 0.98, Output is 54 V DC,62.6 A.
why zero sequence impedance measurement is not applicable for single phase GT
what is differnt between metering CTs an protection CTs
Can XLPE/SWB/PVC (P3) 7C X 2.5mm2 be replaced by Can XLPE/SWB/PVC (P2) 7C X 2.5mm2??? P3 vs P2
what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value
Explain why the Voltage drop will happen in 3 Phase line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)