why we use copper earthing for neutral while for body GI.
Answer / mayur m budh
The neutral earthing is bound to take the maximum possible fault current all the times, so the least voltage drop and the least step potential is desired, however a body earthing, generally depending on its criticality and most of the times connected at tow diagonally opposite points is the main parallel path other than the body or supporting structure itself to carry away any fault current.
Every design has an advantage and copper is less resistive as compared to ferrous, so lesser cross section is required to connect on the neutral of a bushing or a generator.
Is This Answer Correct ? | 4 Yes | 1 No |
Why are the cores of large transformers built up of circular transactions ?
why ct ,cvt should be stored in a vertical position?
No load tap changing transformer working
For what purpose an AVR in generator sensing generator output voltage?and how the sensing is done by AVR?
Why 268hp induction motor taking different current in three different phases? (In which two phase having same current and one having higher value compare to other 2 phases.)
what are the reasons of CT circuit faulty in busbar protection scheme?
HOW MANY EARTHINGS REQUIRED FOR GENERATER
What is meaning of Float Charging of Batteries???
If we feed 230V ac supply to a full wave rectifare, what & how much will be the out put voltage?
What is the Working principle of ELCB and RCCB?
We have Diesel generator of 200KW but load connected to it only 100KW. Pl. brief me about fuel consumption.
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.