if i conncet ct with ct ratio of 600/5 to an energy meter
having ct ratio of 100/5, the reading show by the meter
will correct, if wrong is there any method to calculate
correct value with shown value, if yes please state
it.....
Answers were Sorted based on User's Feedback
If the meter is designed to use a 100/5 ct, it will receive
5 amps when the load is 100 amps. If the ct were a 600/5,
the meter would receive only 1/6 x 5 amps or 0.83 amps
which would be a low reading. You would need to multiply
the reading by 6 to get the correct value. You would likely
not get the the exact reading with the 600/5.
| Is This Answer Correct ? | 3 Yes | 0 No |
What are the weight of 800KV DA,DB and DC type tower ?
if a 3 phase induction stator has charactristic plate and have on winding inside.with the calculation of plate or dimenssion of core how one can desinge rewinding drawing.
How we can design a cable for a 3phase load.
What is the formula to find out cross sectional area of cable for certain current rating?
how vfd drives energy save
why is corona loss greater in a stranded conductor as compared to a solid conductor ?
A FIELD MAGNET IS EXITED BY AC/DC?
How to calculate the cable size in sq. mm. when the load is given in KW?
what is integrated ac contact circuit
what is a core company? why should we join a core company?
Can I use measuring current transformers in protection purposes?
one split ac how can told of this ac which Tr tell me us
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)