if i conncet ct with ct ratio of 600/5 to an energy meter
having ct ratio of 100/5, the reading show by the meter
will correct, if wrong is there any method to calculate
correct value with shown value, if yes please state
it.....
Answers were Sorted based on User's Feedback
If the meter is designed to use a 100/5 ct, it will receive
5 amps when the load is 100 amps. If the ct were a 600/5,
the meter would receive only 1/6 x 5 amps or 0.83 amps
which would be a low reading. You would need to multiply
the reading by 6 to get the correct value. You would likely
not get the the exact reading with the 600/5.
| Is This Answer Correct ? | 3 Yes | 0 No |
how to calculate mf when meter and cTPT detail are given
why only 26v dc is used in aircraft and 115v ac in aircraft.
Why field rheostat is kept in minimum position while armature rheostat at maximum position?
Wht ar the reason for low voltage on consumer side?
In ACS 1000 drive we are using 12 pulse converter,why don't use 3 pulse converter.
how to find insulation resistance of a generator(11kv) by theoritical formula??
why we not using 230kv directly why we are stepping down and then stepping up
how does the thyistor work in dc drive?
What is TR of AC?
what is NGR in generator?
What is The Resistance Formula
Is it possible to get earth resistance value"zero" Ohm practically??? If yes,which type of earthing???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)