if i conncet ct with ct ratio of 600/5 to an energy meter
having ct ratio of 100/5, the reading show by the meter
will correct, if wrong is there any method to calculate
correct value with shown value, if yes please state
it.....
Answers were Sorted based on User's Feedback
If the meter is designed to use a 100/5 ct, it will receive
5 amps when the load is 100 amps. If the ct were a 600/5,
the meter would receive only 1/6 x 5 amps or 0.83 amps
which would be a low reading. You would need to multiply
the reading by 6 to get the correct value. You would likely
not get the the exact reading with the 600/5.
Is This Answer Correct ? | 3 Yes | 0 No |
We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
What are the applications that use Solid State Drives in your home?
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
which type of motor is suitable for lift?
18 Answers NTTF Nettur Technical Training Foundation, Pothigai Power Solutions,
What do we use in Motor core laminations..???CRGO or CRNGO..and why..????
If Earthing is poor in a DB of of Residential Building, will residents feel a leakage voltage in a Electrical Ssytem? is this statement true?
1 Answers Dolphin International,
what is slip ring startor
what is voltage
what will be the motor terminal box connection arrangement (star or delta). on what basis it decided?
how is working d.c amps meter?how to connect the dc ammeter inthe circuite?
Which supply is using for train AC or DC & what is the voltage????????
Why have to use copper cable for local isolator to motor ?