Answer / mike evans
Circuit breakers are designed with withstand short circuit
currents for a short period of time, defined as Icw for a
period of 1 second. This is designed to guarantee
selectivity of breakers and other devices providing short
circuit current protection. The ultimate breaking capacity
of the breaker is the highest symmetrical short circuit
fault current that the breaker is designed to break, and the
breaker manufacture is required to guarantee this level of
performance for one time only. Ics or service breaking
capacity must be guaranteed at least 3 times.
Realistically, the value of Icu is not practical when
considering fault calculations in a distribution system, and
often manufacturers aim for achieving Ics=Icu.
| Is This Answer Correct ? | 147 Yes | 26 No |
Answer / ravikumar varatharaj
Icu - ultimate short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence do not include the capability of the circuit-breaker to carry its rated current continuously
Ics - service short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence include the capability of the circuit-breaker to carry its rated current continuously
Icw - rated short-time withstand current
The rated short-time withstand current of a circuit-breaker is the value of short-time withstand
current assigned
Icm - short-circuit breaking (or making) capacity
a breaking (or making) capacity for which the prescribed conditions include a short circuit
| Is This Answer Correct ? | 40 Yes | 9 No |
Answer / tad rybak
To my understanding Icm stands for Short Circuit Making
Capacity.
According to standard IEC 947-2 or BS EN60947, etc.
It is equal to 2.2 x Icu, where Icu means Ultimate breaking
capacity.
| Is This Answer Correct ? | 53 Yes | 31 No |
Answer / vyara
Ultimate or rated short-circuit breaking capacity
(Icn - EN 60898)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB (Miniature Circuit
Breakers) to carry 0.96 times its rated current for the
conventional time.
Ultimate short-circuit breaking capacity
(Icu - EN 60947-2)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB to carry its
rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60898)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry 0.96
times its rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60947-2)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry its rated
current for the conventional time.
| Is This Answer Correct ? | 19 Yes | 20 No |
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house
why substation are rated like 11KV or 33KV?
3 Answers TNEB Tamil Nadu Electricity Board,
What is the difference between ARC & SPARK?
Now I inject 1kv DC supply r&y=??? R&Y=?? Y&B=?? B&R=???? RYB&N=??? RYBN&E=????? Minimum value====???????
what is the full form of ka (100A mccb KA)
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.
What is the problem if we connect a weak capacitor to the system? is that profitable or Loss?
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
Describe the colour rendering properties of i) tungsten filament lamps ii) tubular fluorescent lamp
reason of capacitor failure or low voltage in alternator wtih 10kva dgset
why a bulb glow when connected with two end phase and neutral respectively.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)