Answer / mike evans
Circuit breakers are designed with withstand short circuit
currents for a short period of time, defined as Icw for a
period of 1 second. This is designed to guarantee
selectivity of breakers and other devices providing short
circuit current protection. The ultimate breaking capacity
of the breaker is the highest symmetrical short circuit
fault current that the breaker is designed to break, and the
breaker manufacture is required to guarantee this level of
performance for one time only. Ics or service breaking
capacity must be guaranteed at least 3 times.
Realistically, the value of Icu is not practical when
considering fault calculations in a distribution system, and
often manufacturers aim for achieving Ics=Icu.
| Is This Answer Correct ? | 147 Yes | 26 No |
Answer / ravikumar varatharaj
Icu - ultimate short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence do not include the capability of the circuit-breaker to carry its rated current continuously
Ics - service short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence include the capability of the circuit-breaker to carry its rated current continuously
Icw - rated short-time withstand current
The rated short-time withstand current of a circuit-breaker is the value of short-time withstand
current assigned
Icm - short-circuit breaking (or making) capacity
a breaking (or making) capacity for which the prescribed conditions include a short circuit
| Is This Answer Correct ? | 40 Yes | 9 No |
Answer / tad rybak
To my understanding Icm stands for Short Circuit Making
Capacity.
According to standard IEC 947-2 or BS EN60947, etc.
It is equal to 2.2 x Icu, where Icu means Ultimate breaking
capacity.
| Is This Answer Correct ? | 53 Yes | 31 No |
Answer / vyara
Ultimate or rated short-circuit breaking capacity
(Icn - EN 60898)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB (Miniature Circuit
Breakers) to carry 0.96 times its rated current for the
conventional time.
Ultimate short-circuit breaking capacity
(Icu - EN 60947-2)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB to carry its
rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60898)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry 0.96
times its rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60947-2)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry its rated
current for the conventional time.
| Is This Answer Correct ? | 19 Yes | 20 No |
how can we avoid magnetostriction in transformer?describe the suitable methods.
What is stray looses?
Can anybody explain me the electrical circuit of indian railways to drive electrical engines(LOCOMOTIVES)? How does overhead lines work in the circuit to drive different trains on the same track?
how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?
what is the use of current transformer in power transformer secondary side.?its connectyed in WTI
why do mostly prefer to generate and distribute electricity in 3 phase..not in 4 phase or 5 phase.??
what is the purpose of measuring % impedence?
what will be d.g. capacity to cater together for 14hp A.C. load & 3kw lighting load
If single phase having 220v so why 3phase is440v.
what are the advantages and disadvantages of speed control of 3 phase induction motor by varying frequency explain with drawing
This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.
what is 33 /11kv transformer bdv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)