Answer / gajanan
there are two losses occure in transformer viz. Cu loss and
iron loss.
Cu loss depends on current & iron loss depends
on voltage and not affected by power fector hence always
transformer ratting defined in KVA not in Kw.
Is This Answer Correct ? | 21 Yes | 3 No |
Answer / prabahakaran
WE know the relation of power in three phase =
√3VIcosØ.hence we can say that the load is not constant it
very accordingly. So power factor is also get vary with
load it is hard to define the power of transformer so it is
rated in KVA.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / gaurav bhardwaj
Rating is any device,s power capacity..so if u know how much useful power u can get then only it will be in kW..bcz power factor plays role in useful power then we can say that if a transformer has 20kva rating then it will deliver 20,kw at pf=1..Nd as we don't know the load which is to be supplied that's y rating in kva ,as kW=kva*pf
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / eng. d
I like the answer which is talking about the cu losses and
characterstic of the transformers.
let me drive the answer from differint angle.
let us assume that we told you that, the transformer is 20
MW, and now you want to connect motor of 15 MW to this
transformer, are you able to start this motor from this
transformer before the protection setting trip the circuit
breaker of the transformer?
I don't really know!! because I don't know how much
reactive power in this transformer, in other words, I don't
know how much losses in this transformer, then I can't do
prpoer analisys of the motor starting without knowing the
MVA rating.(which will include active and reactive power)
my advice, please try to do motor starting analysis on ETAP
or Matlap or any electrical softwaer and play with the
reactive power and see the differance and you will be clear
more ^_*
good luck
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / chinna
trf rating in KVA,current measures in amps&voltages
measures in volts.thats trf rating in kva.
Is This Answer Correct ? | 4 Yes | 11 No |
why do select 11000v rubber mat even we use only 415Volts
1 Answers Saint Gobain, Tata Steel Limited,
what is meant by Back emf ?where its occur ?
why humming sound occured in h HT transmission line
how to calculate ups and battery rating
why we setting 95 deg and 105 deg in wti and oti of distibution transformer ? give the reson for that ?
How to calculate Earth busbar size & what is the procedure we make for determine that?
what is the role of energy meter in distribution system ???? technical and non technical losses in distribution system????
I Just want do EHS Certified Certification Distance Course From Govt approved,so can any body provide me details.
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
what maximum range of star & delta in hp or kw ?
0 Answers Makkah Hilton Towers,
give me applications of sequence bridges . (used in 3 phase un balanced systems)
Dear sir, we are getting voltage fluctuations suddenly for 2 or 3 minutes again it becomes normal. we checked each and every connection some times we are getting 110 volts like that from earth to neutral again it is reducing we are getting supply from 45 kva DG set give earthing properly.