Hi ,what the accurate method to set correct(In) over load to
protect the 3~ motor
Answers were Sorted based on User's Feedback
I follow this method where before setting the overload
current setting I carry out an actual current consumption
test with a clamp ammeter.If the reading is lower than the
rated full load current of the motor I would set it at
actual reading add 5 percent and set it as the tripping
current. But if the the actual consumption is already the
rated fl current or almost it than the setting would be at
the rated full load current of the motor but never exceed
it.This way if it trips at any time than find out the root
cause and than only put into operation.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / joseph
The correct setting of over load relay is 105% of full load current.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / pundlik wanwe
For calculation of thermal over load current setting following formula is used
OLR = Motor FL current/ CT Ratio X 105%
Normally it is set at 105 %
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / simon peter
Firstly u should know the correct ampere of the load which will b drawn. According to rating buy ELCB,M.C.B of that rating .....
Is This Answer Correct ? | 0 Yes | 1 No |
Some times to change of DOR of a motor, interchange of R & B is not effected and RYB take same current, but interchange of R&Y is effected ie change the DOR. My doubt is what is the problem in motor and how it is happen.
If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calculation formula. what extra load have to consider. in what efficiency it will work.
In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected
what ll happen if neutral is not shorted with phases while doing transformer short circuit test & what ll happen if neutral is connected to ground?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
what is mean by potential and potential free contacts
How RTCC panel is working and give single line diagram for RTCC with transformer?
why nutral and earthing wire connect with each other in main panel board.
losses in transmission lines ?
how to produsing geretor power
can we measure +,-.zero sequence current ....? if so how can ???
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt