A group of machines (wind turbines) connected with 33KV
feeder and each machines are having individual VCB. The 33KV
feeder connected with 110KV/33KV substation. The 33KV feeder
tripped by over current at Substation and fault recorded at
Substation as OC-R&Y phase. Same time the group of machines
VCB tripped by over voltage, the fault recorded voltage was
above 66KV by numerical Under/Over voltage relay. While grid
drop time, this much of voltage hike is possible?



A group of machines (wind turbines) connected with 33KV feeder and each machines are having individ..

Answer / k.prakashchandra

The load throw-off may result in run-away speed being equal
to twice the normal speed ,hence the voltage may also become
twice. Over voltage relay should be set at not more than
120%.You can employ the AVR so that the voltage does not
increase with the speed.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

please tell me, how i clear the objective test? when i studied form the one book after i solved the objective ,that time i solved that qes. but if i tried solve objective form the other book then i could not solved these que.

0 Answers  


please explain to me how to calculate current,voltage,resistance with formula??

0 Answers  


for 750 kw LT load what will be the ht kva

0 Answers   Sterling Tools,


power is the product of voltage and current.so we can measure the value of power just by using ammeter and voltmeter.......then why do we use a wattmeter?

5 Answers  


Briefly describe your ideal job?

0 Answers   L&T, LPGCL, ONGC,






Why is remote backup preferred to local backup?

0 Answers  


what happens when power factor leads or lags to electical or home appliances

2 Answers  


Which power will flow first if we switch on a motor Active or Reactive? How?

3 Answers  


why most of the induction are delta connected?

6 Answers  


What does the a,b,c of 95a,95b,95c relays denotes?

0 Answers   KSEB,


What will happen if " not connecting the neutral point to ground of diesel generator output (380 V)", also if someone touched one phase without isolation from ground during the A/M condition what will happen to him?

3 Answers  


What is the difference between grounding & earthing?

9 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)