A 6.6 KV motor breaker is try to Drack OUT by me while the
motor running. What will Happened?
a, will Trip.
b,Drack Out lever will not access
c, will get shock
d, noting will happened
Answers were Sorted based on User's Feedback
Answer / vinayak
For 6.6 KV Motor's VCB haves inbuilt interlock that if you
try to rack out VCB it will trip VCB and naturally trip
Motors. IS/IEC will not permit omit this intelock.
In Case if interlock not working, It will produce arching
and Noise at point of disconnection of contact.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shahid mukhtar
there is a mechanical lock which inhibits breaker to
rackout in case of breaker close. so you cannot rackout
braker in close position.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sri rama murthy
electrical flash can take place as it happened in my
industry
Is This Answer Correct ? | 1 Yes | 1 No |
Do anybody has a design software or tools for the selection and design of electromechanical components???
why pull the single core cable?
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
what is plunger and what's the use of it in motor alignment?
who can measure the size of power cable?
what is power factor? whether it should be high or low? why?
What is meant by directional power and reverse power relay ?
how we can select MCB ratings according to Voltages, Curves.
We in my plant one of the transformer showing neutral to earth voltage is 22V how to solve it
why we use Bus earth truck and Cable earth truck
How dia computation perfomed in cold rolling mills .
3 phase induction motor connection star or delta while using ac drive motor is .75 to 5.5 kw