what is the solution for meger test failed the MV cable?
Answer / arunkumar p
Please check the cable for any damage or puncture on outer
side.
If any damege found, then do necessary cable joint else
replace the cable.
| Is This Answer Correct ? | 4 Yes | 0 No |
In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?
what is PI value and its significance for insulation testing?
how to select earthing conductor size of amy motor/panel etc.
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
DIFFERENCE BETWEEN GROUND AND NEUTRAL?
The unit of resistivity is:(a) ohms(b) ohm millimetre(c) ohm metre(d) ohm/metre
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?
WHY CBCT USE ONLY IN Y PHASE NOT OTHER PHASES
why DG sets power factor is 0.8 lagging.
all types of electrical quations
What are the Safety Steps While Inspection the LT Panel.
75kw drive operated motor current fluctuation from(85-130)ampere.current setting in drive is 130amp.sometimes motor trip when current limit cross 130amps.I change the drive. still current fluctuate between 80-130amps but in this time motor not trip,current setting in drive is 130amps.where is the problem?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)